[RE-wrenches] 210.8

Jason Szumlanski jason at floridasolardesigngroup.com
Thu Mar 20 08:07:12 PDT 2025


210.8 covers GFCI protection for outlets and receptacles. Hard-wired branch
circuits and feeders of a PV and ESS system are not considered outlets or
receptacles.



If I am not mistaken, each subsection specifically mentions outlets and/or
receptacles. Even the section about mini-splits is talking about cord and plug
connected units, not hard-wired appliances.


The entirety of 210 is for branch circuits only, so feeders would not fall under
this section.


Hopefully that helps!

Jason Szumlanski
Principal Solar Designer | Florida Solar Design Group
NABCEP Certified Solar Professional (PVIP)
Florida State Certified Solar Contractor CVC56956
Florida Certified Electrical Contractor EC13013208


On Thu, Mar 20, 2025 at 10:10 AM Lou Russo via RE-wrenches
<re-wrenches at lists.re-wrenches.org> wrote:

> Aloha All,
> 
> 
> My engineer is pushing back on our design, which calls for a battery and load
> center to be installed within 6ft of the water pump and filter, the inverter
> is 7ft away. He is citing NEC 2020 210.8 and the need for GFCI protection. 
> 
> 
> Now besides the practical reason for not doing this, I can not find a code
> reference preventing our proposed location for the battery and load center. 
> 
> 
> This is for an off-grid new construction home with the PV equipment in the
> garage, using a Sol-Ark 15k and Discover Rack Mount batteries. 
> 
> 
> Any input?
> 
> 
> Aloha,
> 
> 
> Lou Russo 
> Owner
> lou at spreesolarsystems.com [lou at spreesolarsystems.com]
> Office - 808 345 6762
> Spree Solar Systems LLC 
> CT-34322
> 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org [http://re-wrenches.org]
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> [RE-wrenches at lists.re-wrenches.org]
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> [http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org]
> 
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> [https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/]
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> [http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org]
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> [http://www.re-wrenches.org/etiquette.htm]
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org [http://www.members.re-wrenches.org]
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250320/127abff1/attachment.htm>


More information about the RE-wrenches mailing list