[RE-wrenches] AGM battery recommendations
Dan Fink
danbob88 at gmail.com
Sun Jan 12 13:33:52 PST 2025
Jeff, this is the most recent document I have on the topic.
The video frame capture pic of the flying garage door hitting the fire
chief is pretty dramatic. But yes some incidents were DIY lithium battery
banks, some were EVs+chargers, etc. I don't think I've seen an official
after-action incident report yet about any UL-9540 compliant lithium
battery install causing a fire.
https://www.iaff.org/wp-content/uploads/IAFF_DOE_ResidentialESSConsiderations_Final.pdf
Dan Fink
Owner, Buckville Energy Consulting LLC
IREC Certified Instructor for PV and Small Wind Installation
NABCEP Certified PV System Inspector
NABCEP PV Associate
d <dan.fink at greendustrialtraining.com>anbob88 at gmail.com
970-672-4342
On Sun, Jan 12, 2025 at 2:20 PM Jeff Clearwater via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Have there been any LFP catastrophic fires that weren’t homemade packs or
> bicycle packs without quality BMSs?
>
> All the fires I ‘ve heard of are LiPo or LiNMC - not LFP.
>
> Best
>
> Jeff
>
>
>
> Sent from my iPhone
>
> On Jan 12, 2025, at 12:55 PM, Jay via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> You guys are making my point.
> Melting the cases is not a fire. And every melted agm case is due to
> incorrect charging mechanisms.
>
> But there have been some cases on this site of catastrophic lithium
> failures.
>
> I am starting to see people asking about fires and lithium.
>
> These batteries are in the house. Not my design and not an easy fix to
> move them.
>
> Thanks again
>
> Jay
>
>
>
> On Jan 12, 2025, at 10:52 AM, Tyrone Houck via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> I had the exact same thing happen(even down to the crowbar) with the only
> set of full river 400 6's I've ever installed. I personally lean away from
> agm though we've had pretty good luck with the Outback and Northstar PLR
> platform over the year..
>
>
>
>
> On Sun, Jan 12, 2025, 9:39 AM Ray Walters via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> The only thermal runaway event I've ever seen, was with AGM in an over
>> insulated battery box. Got so hot that the cases fused to each other, and
>> we had to pry the batteries apart with a crow bar. She wants ZERO risk of
>> fire? She needs to live in a concrete bunker with no electricity at all.
>> Every electrical connection, every outlet, every appliance has a risk of
>> fire. Period.
>>
>> Ray Walters
>> Remote Solar
>> On 1/12/2025 9:39 AM, Tyrone Houck via RE-wrenches wrote:
>>
>> I hate to be the one to say it but LFP has arguably less fire risk than
>> agm. A short circuit in an agm could be disastrous and AGM is not
>> necessarily any safer or less prone to thermal runaway events than modern
>> LFP. I'd recommend a cobalt free LFP like homegrid, simpliphi, or midnite
>> if it were me..
>>
>>
>>
>>
>> On Sat, Jan 11, 2025, 3:38 PM jay via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> I was going to try and steer her towards lithium but she wants zero,
>>> absolutely zero chance of fire, so no lithium.
>>>
>>> great batteries though
>>>
>>> jay
>>>
>>>
>>>
>>> On Jan 11, 2025, at 4:35 PM, MD Electric & Solar via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>> 30KWH of LFP from discover energy, fits in one enclosure, around
>>> $14000.00
>>> Enclosure is indoor/outdoor rated.
>>>
>>> https://discoverenergysys.com/products/lithium-batteries/aes-rackmount
>>> https://discoverenergysys.com/products/accessories/slimline-enclosure
>>>
>>> On Sat, Jan 11, 2025 at 3:31 PM jay via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> HI Willam
>>>>
>>>> Thanks for the input.
>>>> I didn’t know that trojan was sold, and from what you say, yeah scratch
>>>> them off.
>>>>
>>>> It’s currently at 30kwh. And thats probably a good size.
>>>> As always, cost and time is a factor.
>>>>
>>>> I’ll check the others out.
>>>>
>>>> jay
>>>>
>>>>
>>>>
>>>>
>>>>
>>>> > On Jan 11, 2025, at 4:17 PM, William Miller <william at millersolar.com>
>>>> wrote:
>>>> >
>>>> > Jay:
>>>> >
>>>> > What AH or Kwh level are you looking for?
>>>> >
>>>> > Trojan was acquired by another company a few years ago and quality
>>>> had gone
>>>> > downhill.
>>>> >
>>>> > Rolls is very sensitive to high temperatures. They will deny a
>>>> warranty
>>>> > claim if all of your parameters are not exactly right.
>>>> >
>>>> > For larger AH systems:
>>>> >
>>>> > I like the Full River DC-400-2. You might be able to do a one string
>>>> > installation.
>>>> >
>>>> > Unigy II is a great system. Very robust. Hard to deliver but I can
>>>> offer
>>>> > tips. Lots of AH size options.
>>>> >
>>>> > William
>>>> >
>>>> > Miller Solar
>>>> > 17395 Oak Road, Atascadero, CA 93422
>>>> > 805-438-5600
>>>> > www.millersolar.com
>>>> > CA Lic. 773985
>>>> >
>>>> >
>>>> >
>>>> > -----Original Message-----
>>>> > From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
>>>> On
>>>> > Behalf Of jay via RE-wrenches
>>>> > Sent: Saturday, January 11, 2025 2:48 PM
>>>> > To: RE-wrenches
>>>> > Cc: jay
>>>> > Subject: [RE-wrenches] AGM battery recommendations
>>>> >
>>>> > Hi All
>>>> >
>>>> > I have a customer what is set on AGM.
>>>> >
>>>> > It been so long since I’ve bought any, wondering if there are any
>>>> > recommendations?
>>>> >
>>>> > The ones I’m looking at:
>>>> >
>>>> > Rolls S6-460AGM-RE
>>>> >
>>>> > Full river DC-400-6
>>>> >
>>>> > Trojan SAES 06 375 6V
>>>> >
>>>> > sun Xtender brand.
>>>> >
>>>> > What’s interesting is the trojan has about 3000 cycles vs the others
>>>> at
>>>> > around 1250 cycles to 50%.
>>>> > Im wondering if that is a marketing idea or if its real.
>>>> >
>>>> > thanks in advance
>>>> >
>>>> > jay
>>>> > _______________________________________________
>>>> > List sponsored by Redwood Alliance
>>>> >
>>>> > Pay optional member dues here: http://re-wrenches.org
>>>> >
>>>> > List Address: RE-wrenches at lists.re-wrenches.org
>>>> >
>>>> > Change listserver email address & settings:
>>>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> >
>>>> > There are two list archives for searching. When one doesn't work, try
>>>> the
>>>> > other:
>>>> > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> >
>>>> > List rules & etiquette:
>>>> > http://www.re-wrenches.org/etiquette.htm
>>>> >
>>>> > Check out or update participant bios:
>>>> > http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>>
>>>
>>> --
>>> Michael D Nelson
>>> MD Electric & Solar Inc.
>>> Office: 707-412-3181
>>> Cell: 707-684-0064
>>> www.mdelectricsolar.com
>>> www.facebook.com/mdelectricandsolar
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:http://www.members.re-wrenches.org
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250112/84a42deb/attachment.htm>
More information about the RE-wrenches
mailing list