[RE-wrenches] AGM battery recommendations

solareagle at solareagle.com solareagle at solareagle.com
Sun Jan 12 13:13:54 PST 2025


One comment with regard to Rolls AGM’s. I, like yourself, have sold very few AGM’s over the years, preferring lead acid. But I supplied a set of Rolls AGM’s to a client who self installed and didn’t recognize the need for a minimum 85a charge. His inverter/pv combination was unable to supply that and the batteries sulphated within months to an unrecoverable state. $20k down the drain. Most other AGM’s get by with around 50a charge.

Ron

> On Jan 12, 2025, at 12:55 PM, Jay via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
> You guys are making my point. 
> Melting the cases is not a fire. And every melted agm case is due to incorrect charging mechanisms. 
> 
> But there have been some cases on this site of catastrophic lithium failures. 
> 
> I am starting to see people asking about fires and lithium. 
> 
> These batteries are in the house. Not my design and not an easy fix to move them. 
> 
> Thanks again
> 
> Jay 
> 
> 
> 
>> On Jan 12, 2025, at 10:52 AM, Tyrone Houck via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>> 
>> 
>> I had the exact same thing happen(even down to the crowbar) with the only set of full river 400 6's I've ever installed. I personally lean away from agm though we've had pretty good luck with the Outback and Northstar PLR platform over the year..
>> 
>> 
>>    
>> 
>> On Sun, Jan 12, 2025, 9:39 AM Ray Walters via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>> The only thermal runaway event I've ever seen, was with AGM in an over insulated battery box.  Got so hot that the cases fused to each other, and we had to pry the batteries apart with a crow bar.  She wants ZERO risk of fire?  She needs to live in a concrete bunker with no electricity at all.  Every electrical connection, every outlet, every appliance has a risk of fire.  Period.
>>> 
>>> Ray Walters
>>> Remote Solar
>>> 
>>> On 1/12/2025 9:39 AM, Tyrone Houck via RE-wrenches wrote:
>>>> I hate to be the one to say it but LFP has arguably less fire risk than agm. A short circuit in an agm could be disastrous and AGM is not necessarily any safer or less prone to thermal runaway events than modern LFP. I'd recommend a cobalt free LFP like homegrid, simpliphi, or midnite if it were me..
>>>> 
>>>> 
>>>>    
>>>> 
>>>> On Sat, Jan 11, 2025, 3:38 PM jay via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>>> I was going to try and steer her towards lithium but she wants zero, absolutely zero chance of fire, so no lithium.
>>>>> 
>>>>> great batteries though
>>>>> 
>>>>> jay
>>>>> 
>>>>> 
>>>>> 
>>>>>> On Jan 11, 2025, at 4:35 PM, MD Electric & Solar via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>>>> 
>>>>>> 30KWH of LFP from discover energy, fits in one enclosure, around $14000.00
>>>>>> Enclosure is indoor/outdoor rated.
>>>>>> 
>>>>>> https://discoverenergysys.com/products/lithium-batteries/aes-rackmount
>>>>>> https://discoverenergysys.com/products/accessories/slimline-enclosure
>>>>>> 
>>>>>> On Sat, Jan 11, 2025 at 3:31 PM jay via RE-wrenches <re-wrenches at lists.re-wrenches.org <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>>>>>> HI Willam 
>>>>>>> 
>>>>>>> Thanks for the input.
>>>>>>> I didn’t know that trojan was sold, and from what you say, yeah scratch them off.  
>>>>>>> 
>>>>>>> It’s currently at 30kwh.  And thats probably a good size.  
>>>>>>> As always, cost and time is a factor.  
>>>>>>> 
>>>>>>> I’ll check the others out.
>>>>>>> 
>>>>>>> jay
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> 
>>>>>>> > On Jan 11, 2025, at 4:17 PM, William Miller <william at millersolar.com <mailto:william at millersolar.com>> wrote:
>>>>>>> > 
>>>>>>> > Jay:
>>>>>>> > 
>>>>>>> > What AH or Kwh level are you looking for?
>>>>>>> > 
>>>>>>> > Trojan was acquired by another company a few years ago and quality had gone
>>>>>>> > downhill.
>>>>>>> > 
>>>>>>> > Rolls is very sensitive to high temperatures.  They will deny a warranty
>>>>>>> > claim if all of your parameters are not exactly right.
>>>>>>> > 
>>>>>>> > For larger AH systems:
>>>>>>> > 
>>>>>>> > I like the Full River DC-400-2.  You might be able to do a one string
>>>>>>> > installation.
>>>>>>> > 
>>>>>>> > Unigy II is a great system.  Very robust.  Hard to deliver but I can offer
>>>>>>> > tips.  Lots of AH size options.
>>>>>>> > 
>>>>>>> > William
>>>>>>> > 
>>>>>>> > Miller Solar
>>>>>>> > 17395 Oak Road, Atascadero, CA 93422
>>>>>>> > 805-438-5600
>>>>>>> > www.millersolar.com <http://www.millersolar.com/>
>>>>>>> > CA Lic. 773985
>>>>>>> > 
>>>>>>> > 
>>>>>>> > 
>>>>>>> > -----Original Message-----
>>>>>>> > From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org <mailto:re-wrenches-bounces at lists.re-wrenches.org>] On
>>>>>>> > Behalf Of jay via RE-wrenches
>>>>>>> > Sent: Saturday, January 11, 2025 2:48 PM
>>>>>>> > To: RE-wrenches
>>>>>>> > Cc: jay
>>>>>>> > Subject: [RE-wrenches] AGM battery recommendations
>>>>>>> > 
>>>>>>> > Hi All
>>>>>>> > 
>>>>>>> > I have a customer what is set on AGM.
>>>>>>> > 
>>>>>>> > It been so long since I’ve bought any, wondering if there are any
>>>>>>> > recommendations?
>>>>>>> > 
>>>>>>> > The ones I’m looking at:
>>>>>>> > 
>>>>>>> > Rolls  S6-460AGM-RE
>>>>>>> > 
>>>>>>> > Full river DC-400-6
>>>>>>> > 
>>>>>>> > Trojan SAES 06 375 6V
>>>>>>> > 
>>>>>>> > sun Xtender  brand.
>>>>>>> > 
>>>>>>> > What’s interesting is the trojan has about 3000 cycles vs the others at
>>>>>>> > around 1250 cycles to 50%.
>>>>>>> > Im wondering if that is a marketing idea or if its real.
>>>>>>> > 
>>>>>>> > thanks in advance
>>>>>>> > 
>>>>>>> > jay
>>>>>>> > _______________________________________________
>>>>>>> > List sponsored by Redwood Alliance
>>>>>>> > 
>>>>>>> > Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>>>>>>> > 
>>>>>>> > List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>> > 
>>>>>>> > Change listserver email address & settings:
>>>>>>> > http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>> > 
>>>>>>> > There are two list archives for searching. When one doesn't work, try the
>>>>>>> > other:
>>>>>>> > https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>>> > http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>> > 
>>>>>>> > List rules & etiquette:
>>>>>>> > http://www.re-wrenches.org/etiquette.htm
>>>>>>> > 
>>>>>>> > Check out or update participant bios:
>>>>>>> > http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>>> 
>>>>>>> _______________________________________________
>>>>>>> List sponsored by Redwood Alliance
>>>>>>> 
>>>>>>> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>>>>>>> 
>>>>>>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>>> 
>>>>>>> Change listserver email address & settings:
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>> 
>>>>>>> There are two list archives for searching. When one doesn't work, try the other:
>>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>> 
>>>>>>> List rules & etiquette:
>>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>> 
>>>>>>> Check out or update participant bios:
>>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> 
>>>>>> -- 
>>>>>> Michael D Nelson
>>>>>> MD Electric & Solar Inc.
>>>>>> Office: 707-412-3181
>>>>>> Cell: 707-684-0064
>>>>>> www.mdelectricsolar.com <http://www.mdelectricsolar.com/>
>>>>>> www.facebook.com/mdelectricandsolar <http://www.facebook.com/mdelectricandsolar>
>>>>>> 
>>>>>> 
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>> 
>>>>>> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>>>>>> 
>>>>>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>>> 
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> There are two list archives for searching. When one doesn't work, try the other:
>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>> 
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>> 
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>>> 
>>>>> 
>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>> 
>>>>> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>>>>> 
>>>>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>>>> 
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>> 
>>>>> There are two list archives for searching. When one doesn't work, try the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>> 
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>> 
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>>> 
>>>> 
>>>> 
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>> 
>>>> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>>>> 
>>>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>>> 
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>> 
>>>> There are two list archives for searching. When one doesn't work, try the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>> 
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>> 
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>>> 
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>> 
>>> Pay optional member dues here: http://re-wrenches.org <http://re-wrenches.org/>
>>> 
>>> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>>> 
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>> 
>>> There are two list archives for searching. When one doesn't work, try the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>> 
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>> 
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
>>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> Pay optional member dues here: http://re-wrenches.org
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> 
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250112/df556c2b/attachment.htm>


More information about the RE-wrenches mailing list