[RE-wrenches] Alternate LVD shutdown
Mac Lewis
maclewis1 at gmail.com
Thu Jan 2 17:53:04 PST 2025
Hi Bill,
Are all your voltages calibrated? Mate, Flexmax, FM80? Where are you
reading the voltages?
Does it work OK manually?
On Thu, Jan 2, 2025 at 12:08 PM Jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Simpliphy has a very high voltage LVD.
> And the older OB can’t be programmed to those voltages
>
>
>
> On Jan 2, 2025, at 10:04 AM, Tyrone Houck via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Forgive my ignorance but why won't the vfx lbco work for lithium?
>
>
>
>
> On Thu, Jan 2, 2025, 8:19 AM Bill Battagin via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> I am trying to use the "low battery disconnect" in aux mode in a newly
>> installed OB FM80 CC for Li battery low voltage protection. I can't use
>> the 19 year old OB VFX inverters for obvious reasons. The plan is to run
>> the 12 volt output from the aux output to a NC relay to open it at 50
>> VDC of the bank of SimpliPhi 3.8M batteries. 50 VDC is SimpliPhi's
>> recommendation for LVD. The "output" of the relay would be connected to
>> the VFX's ON-OFF landings of that little green terminal block in the AC
>> side of the inverter and just act as a simple switch for the inverter to
>> turn it off to save the batteries.
>>
>> I'm using one of my newer FM80's as a test run and have
>> programmed the voltages in Low Battery Disconnect mode and then put it
>> in auto mode. However, as the CC goes below the voltage set point, the
>> AUX output does not turn on (time set for 5 seconds), as evidence in the
>> CC's home screen and by checking for 12V at the AUX terminal block.
>>
>> Any ideas of what I'm missing here to make this work? I
>> know the other solution, thousands of $$ for new inverters which would
>> be great but these folks have already invested quite a chuck on array
>> replacement and charge controllers.
>>
>> Thanks for any experience with this.
>>
>> Bill
>>
>> Feather River Solar Electric
>> Bill Battagin, owner
>> 4291 Nelson St. (Shipping)
>> 5575 Genesee Rd
>> <https://www.google.com/maps/search/5575+Genesee+Rd?entry=gmail&source=g>.
>> (USPS, UPS)
>> Taylorsville, CA 95983
>> 530-284-7849, 258-1641(cell)
>> CA. C10 Lic # 874049
>> Solar Powered since 1982
>> Home of the Sunny Side Up
>>
>>
>> --
>> This email has been checked for viruses by Avast antivirus software.
>> www.avast.com
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Mac Lewis
*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20250102/effa703c/attachment.htm>
More information about the RE-wrenches
mailing list