Much appreciated.   Thank you, Chris

On 11/15/2024 8:27 AM, Poole, Jharen wrote:
> Hello Chris,
>
> Stage 0 is what we would consider the state of the inverter before it 
> reaches normal. Once you reach normal (stage 1) that is when you will 
> begin outputting power, inverting power from solar, etc.
>
>
> Best Regards,
>
> Jharen Poole
> Applications Engineer II
> 972-575-8875
> ------------------------------------------------------------------------
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on 
> behalf of Christopher Warfel via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org>
> *Sent:* Thursday, November 14, 2024 8:37 AM
> *To:* re-wrenches at lists.re-wrenches.org 
> <re-wrenches at lists.re-wrenches.org>
> *Cc:* Christopher Warfel <cwarfel at entech-engineering.com>
> *Subject:* Re: [RE-wrenches] More Issues with Parallel Sol-Ark 15K System
>
> 	
> Caution: This email is from an external source.
>
>
>
> Can you point to a reference to what stage 0 is?  This is a new term 
> for me. So far, have not installed multiple Sol-Ark inverters at one 
> site.  Thank you, Chris
>
> On 11/12/2024 12:50 PM, Poole, Jharen via RE-wrenches wrote:
>> Our inverters utilize CANbus communications for establishing parallel 
>> operation between multiple Sol-Ark inverters. CANbus communication 
>> operates as a serial communication protocol. In this setup each 
>> inverter in the setup is linked via a parallel communication cable 
>> forming a daisy-chain configuration. If one inverter in the chain 
>> experiences a shutdown due to a fault, the communication chain is 
>> disrupted. Consequently, the other inverters will also power down 
>> when we see this loss, ensuring system protection and safeguarding 
>> the customer’s investment.
>>
>> Paralleling must be done at a stage 0 they have to sync and that is 
>> done in the pre normal mode, functionality wise having them going 
>> into sync is extremely difficult due to timing issues. It's easier to 
>> time it from a stage 0 than to do it when one unit is already running.
>>
>> Maintaining synchronization between inverters is critical; if the 
>> inverters were to operate out of parallel it can result in conflicts 
>> between the operation of inverters and desynchronization of the 
>> units. This misalignment can escalate, potentially causing 
>> significant damage to one or more inverters and risking harm to other 
>> connected equipment.
>>
>>
>> Best Regards,
>>
>> Jharen Poole
>> Applications Engineer II
>> 972-575-8875
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here:http://re-wrenches.org  <http://re-wrenches.org>
>>
>> List Address:RE-wrenches at lists.re-wrenches.org  <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org  <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/  <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org  <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm  <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org  <http://www.members.re-wrenches.org>
>>
> -- 
> Christopher Warfel, PE
> Entech Engineering, Inc.
> POB 871 Block Island, RI 02807
> 401-447-5773
-- 
Christopher Warfel
           ENTECH Engineering Inc.
    PO Box 871, Block Island, RI 02807
                   401-477-5773
EE Logo <https://entech-engineering.com/Home/default.php>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241115/fa230d93/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-d3rjq53y.png
Type: image/png
Size: 82002 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241115/fa230d93/attachment-0002.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: Outlook-glvzpbsr.png
Type: image/png
Size: 82002 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241115/fa230d93/attachment-0003.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241115/fa230d93/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: cwarfel.vcf
Type: text/vcard
Size: 203 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241115/fa230d93/attachment-0001.vcf>


More information about the RE-wrenches mailing list