[RE-wrenches] OB Charging/Comms Issues
jay
jay.peltz at gmail.com
Fri Nov 8 13:13:49 PST 2024
Hi Chris,
Is this new or has it been always like this?
jay
> On Nov 8, 2024, at 1:42 PM, Chris Sparadeo via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
> Hey wrenchers,
>
> I have an off-grid customer with a pair of VFX 3648 inverters, a FM 100 charge controller and two eVault classics in open loop. The issue is when the generator is charging the batteries, incoming amperage is all over the place and periodically, gradually drops to 0A then ramps back up. This is creating really long generator run times. When I turn off PV input, same results. When I turn off both PV input and charge controller output (turning off the CC entirely) the inverters hold a steady charge. If I remove the charge controllers comms cable from the hub, they both play nicely and charge cooperatively. This obviously sounds like a communication issue, but unfortunately, without the help of OB tech support, I am left speculating. I have checked all settings with a fine comb and nothing looks to be out of place. Has anyone experienced something similar to this?
>
> Thanks!
>
> Chris Sparadeo
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list