[RE-wrenches] washer on OutBack inverter

William Miller william at millersolar.com
Mon Oct 21 11:42:54 PDT 2024


Kevin:



Your experience sounds a lot like a similar one we had with a Radian
system.  It is documented here
<https://millersolar.com/MillerSolar/case_studies/25_GFI%20Tripping/GFI_Tripping.html>
along with the solution we found.  I hope you find some value in our case
study.



William



Miller Solar

17395 Oak Road, Atascadero, CA 93422

805-438-5600

www.millersolar.com

CA Lic. 773985





*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Kevin Pegg via RE-wrenches
*Sent:* Monday, October 21, 2024 11:27 AM
*To:* RE-wrenches
*Cc:* Kevin Pegg
*Subject:* Re: [RE-wrenches] washer on OutBack inverter



We have had issues with older FX / VFX Outback inverters not reliably
operating some appliances with electronic controls when the generator is
running and charging batteries. Unsure if Radian corrected that. Loads ok
on inverter, ok on generator direct, but charging – problems. It’s a known
issue with harmonics from the charging circuit. It became enough of a
problem that we stopped recommending Outback for full time off-grid clients
where generator use is a reality in the winter months. Had to replace
several units with another brand.



Kevin



*From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> *On Behalf
Of *David Palumbo via RE-wrenches
*Sent:* October-21-24 8:12 AM
*To:* Wrench List <re-wrenches at lists.re-wrenches.org>
*Cc:* David Palumbo <palumbo131m at gmail.com>
*Subject:* [RE-wrenches] washer on OutBack inverter



Wrenches,



I need to replace a front load washer in my off grid rental house.



Looking at LG's and I'm wondering if any of you have experience with them
running on OutBack inverter power.



The Maytag washer I'm replacing ran fine on inverter power but would not
operate on Generac Eco-Gen power.



Dave Palumbo

Hyde Park, Vermont

802-371-8678 voice or text
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241021/b43901b5/attachment.htm>


More information about the RE-wrenches mailing list