sounds strange to me. is the service 120 208 meaning 120 to neutral, and
120 to neutral and 208 between phases? meaning you are two legs of a
3-phase? if you are trying to use a single phase 240 volt inverter, be
careful of the inverter wiring. some inverters can not be connected
because you do not have a single phase .
On Thu, Oct 17, 2024 at 12:02 PM Steven Lawrence via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> This is very common in and around the NYC area. You'll need a 240V to
> 208V transformer. It'll be faster and nowhere near as expensive as paying
> ConEd to drop a new bucket transformer for you.
> On future projects, be sure to look at the electrical service
>
> Steven Lawrence
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20241017/0c356d67/attachment.htm>
More information about the RE-wrenches
mailing list