[RE-wrenches] OB Radian / FM60 grid tie mystery
Kirk Herander
kirkh at vermont.solar
Mon Sep 16 16:30:24 PDT 2024
Solved the problem.
Somehow the "sell current limit" in the grid interface protection menu, a
hidden menu only accessed by creating a new installer login code, was set
to 7.5 a.
I reset it to the max of 30a, and the system sells normally again.
I read on an outback forum this parameter can change as a result of a
GS8048 firmware upgrade. Go figure.
On Sun, Aug 18, 2024 at 1:11 PM Kirk Herander <kirkh at vermont.solar> wrote:
> Hello All,
> .
> I have a Radian 8048 system in service for over 10 years now. It sold back
> quite normally until the last several months -3.- FM60 CC's are set to grid
> tie mode and viewable and programmed from the Mate3s / OpticsRE. This
> issue loosely correlates to replacing one of the CCs several months ago.
>
> Trouble is all -3- charge controllers are almost always in a float mode.
> The radian does sell, but at a small KW compared to what it used to before
> the frequent float mode started popping up. If I remember correctly,
> ideally the CCs should always be in bulk charge when sellback occurs.
>
> I have the CC and inverter charger float set to about 1 vdc higher then
> the inverter's sell volts, as I believe was recommended way back when. Hard
> to understand what changed, but something did. I've checked the relevant
> setpoints many times and can't find anything obviously amiss.
>
> Does a sell mode tech note paper exist still for the Radian system? Did it
> ever? Any ideas would be greatly appreciated.
>
>
>
>
> --
>
> *Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
>
> *Owner|Principal, VT Solar, LLC*
>
> *Celebrating our 33st Anniversary 1991-2024!!*
>
> dba Vermont Solar Engineering
>
> 802.559.1225
>
--
*Kirk Herander / **kirkh at vermont.solar <kirkh at vermont.solar>*
*Owner|Principal, VT Solar, LLC*
*Celebrating our 33st Anniversary 1991-2024!!*
dba Vermont Solar Engineering
802.559.1225
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240916/c5052b34/attachment.htm>
More information about the RE-wrenches
mailing list