[RE-wrenches] Schneider mppt 60-150 question

Kevin Pegg kpegg at energyalternatives.ca
Tue Sep 3 11:53:32 PDT 2024


I've got a few installs with the XWMPPT60-150 with Lithium. Deka Duration, closed loop via Insight Home, programmed to allow BMS voltage to drive the MPPT. Have several of this configuration. 

One site upon initial setup was giving constant High Voltage mid day shutdowns on the inverter when batteries at 100% (SW4048) despite logging not showing battery voltage going above 54V. Schneider tech support was beyond useless waste of time. Only way I got this to stabilize was setting the inverter High Voltage shut down to 60V. 58V was still getting the error intermittently. Not ideal but at least the client wasn't having their cooling units without power until they got home from work to reset the inverter. 

Kevin


-----Original Message-----
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Jay via RE-wrenches
Sent: August-30-24 1:53 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Jay <jay.peltz at gmail.com>
Subject: [RE-wrenches] Schneider mppt 60-150 question


Hi all. 

Any issues with the xw 60-150 operating lithium batteries?  
Namely that they are fast enough in their regulation 

Thx
Jay
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



More information about the RE-wrenches mailing list