[RE-wrenches] Fortress Shutdown?
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Tue Aug 27 16:43:01 PDT 2024
Just curious what high SoC is? I set mine for 95% or so and do not
worry about the last few %.
Have not seen this problem but do not use fortress. Should not have shut
downs offgrid except LBCO or lightning.
I really think that an SPD should be on the battery as well as AC in and
out these days,
especially with a 48V BMS. Tempting the demons!
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[1]https://offgridsolar1.com/ [2] [1]
e-mail offgridsolar at sti.net
text 209 813 0060
On 2024-08-27 4:19 pm, Maverick Brown via RE-wrenches wrote:
> Ray
>
> I think you are on to something.
>
> I have multiple eVault MAX batteries on a Radian and I have had
> mysterious random shutdowns with high SOC before.
>
> Could be they were off grid at the time or had a big load shut off
> causing a voltage bounce.
>
> The batteries are comm'd together but not to the Radian, of course.
>
> If that is the case, I wonder if there is a newer battery firmware that
> can over come this or in fact why a LiFePO4 can't go over 55.2 when
> most have a 58.4V limit.
>
> Thank you,
>
> Maverick
>
> Maverick Brown
> Off-Grid Solar Commander since 2006
> Maverick Solar Enterprises, Inc.
> * Solar Commander Remote Power
> * SunFlow Systems Cathodic Protection
> maverick at mavericksolar.com
> 512-460-9825
>
>> On Aug 27, 2024, at 5:24 PM, Ray Walters via RE-wrenches
>> <re-wrenches at lists.re-wrenches.org> wrote:
>
> Is it possible that a load shut off, and then the controllers over shot
> the voltage long enough to shut the BMS off? If so, what's the
> solution? Lower absorb voltages? I checked voltage calibration between
> the various pieces of equipment.
>
> Ray
>
> On 8/27/2024 4:14 PM, Jerry Shafer via RE-wrenches wrote:
>
> High voltage disconnect would do this, is the site monitored
>
> Fun times
>
> On Tue, Aug 27, 2024, 2:47 PM jay via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
> I have a buddy in tech support at Fortress.
>
> I asked him and he said that elevated absorb volts above 55.2 could
> cause this situation.
> And then the power cycle would reboot the BMS.
>
> I am presuming its open loop, and the fact you mentioned that there was
> more PV and then the shut down sure might be connected.
> You might check the charge voltages/time to make sure they are correct
> and I can't remember if the classic has battery sense wire connections.
>
> jay
>
> On Aug 27, 2024, at 2:51 PM, Ray Walters via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> The SPD was on one of the PV inputs before it came into the house.
> There were two Classics, each fed with its own PV input and SPD. It
> actually caused an underground splice to fail (high resistance) which I
> replaced the splice and restored full voltage, and both Classics were
> working fine. Just seems unlikely ( but not impossible) that the surge
> would make it past the Classic without damage, but then damage the
> Fortress BMS in an otherwise imperceptible manner. That is our
> current best theory at the moment though. I added an SPD on the 48 v
> buss, before this latest total shutdown.
>
> Ray Walters
>
> On 8/27/2024 2:35 PM, Dave Angelini Offgrid Solar via RE-wrenches
> wrote:
> When I have had someone lose an SPD (I assume it was on DC buss) there
> is often latent damage (shows up later) to many of the devices. In a
> Hi Rel mode, it is recommended to replace it all. Most offgrid is not
> that critical but try telling that to someone with rotten food.
>
> The freezers and reefers are often full of spoils that smells never go
> away. YUK !
>
> Dave Angelini Offgrid Solar
> "we go where powerlines don't"
> [1]https://offgridsolar1.com/ [2] [1]
> e-mail offgridsolar at sti.net
> text 209 813 0060
>
> On 2024-08-27 1:02 pm, Ray Walters via RE-wrenches wrote:
> Greetings All;
>
> I have Fortress Battery installation with a pair of E Vault batteries
> set up in a Master/ Slave arrangement. Its been working fine for over
> a year, but the customer just had a complete shutdown of the batteries
> which left multiple freezers, and refrigerator with rotting food.
> When he rebooted the batteries by turning on/off the main breaker on
> each, they both come up and showed 100% SOC on the Master, and 98% on
> the other. There were no fault codes. I just recently installed a
> larger PV array, and so the system has been reaching full charge every
> morning.
>
> I have multiple calls in to Fortress, but not hearing anything back
> from them at all. We did have a lightning surge event a few months
> ago, that damaged a Midnite SPD (first ever for me), and took out the
> control board on the generator. One VFX inverter has an LED out, but
> we only use two inverters of the Quad stack, so I just switched to
> another inverter. All other equipment appeared fine: Midnite
> controllers, rest of the Outback VFX quad stack, and never any issues
> seen with the Fortress batteries.
>
> The other odd thing, is since he rebooted the batteries, the system is
> working fine, and recharging to 100% by 9:30 am as before. Is it
> possible the Fortress BMS were damaged and are now having an
> intermittent shutdown issue? I did ask him to temporarily disconnect
> the comms between batteries, in case it is a bad BMS on one, it will
> isolate it from the other.
>
> This is a tough one to figure out, since it hasn't happened again, and
> there are no fault codes. The Mate 3 shows a low frequency AC code,
> but that's usually just from the generator shutting down. Any help,
> ideas, experiences, would be greatly appreciated.
>
> Thanks,
>
> Ray Walters
> Remote Solar
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org [3]
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org [4]
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org [3]
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org [4]
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Links:
------
[1] http://members.sti.net/offgridsolar/
[2] https://offgridsolar1.com/
[3] http://re-wrenches.org/
[4] http://www.members.re-wrenches.org/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240827/c0824825/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: aa spd.JPG
Type: image/jpeg
Size: 76080 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240827/c0824825/attachment-0001.jpe>
More information about the RE-wrenches
mailing list