[RE-wrenches] AGM blew on discharge
Steve Higgins
steve at surrette.com
Wed Jul 24 08:04:17 PDT 2024
Wrenches,
The S6-460AGM still gasses about 6 liters of hydrogen per battery per hour
while being charged at 2.35vpc or higher, in warmer temperatures, this
gassing accelerates. at 40 C this gassing rates double. In AGM
batteries there is a pressure vent that allows the battery to gas in these
conditions.
If you don't have ventilation or this hydrogen gas is ignited it can and
will trace back to the battery with the highest concentration of gas, and
once it finds compression it'll cook off like a firecracker.
It's a good idea to at least have passive ventilation on AGM while FLA
needs active ventilation, in warmer locations it's a good idea to have some
active ventilation (Cooling helps too) instead of just passive ventilation.
I still see a lot of FLA or AGM batteries being installed directly under
the inverters, chargers or charge controllers... Hydrogen gasses are
lighter than air, so the gas tends to rise vertically. If this gas gets
into the power electronics it can cause corrosion within the power
electronics and if you get a spark from a relay transition you could get an
ignition of the hydrogen gasses causing the battery to blow its top.
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
<http://www.rollsbattery.com> <http://www.rollsbattery.com>
Steve Higgins ⋅ Technical Services Manager
t +1.902.597.4020 m +1.206.790.5840
f +1.902.597.8447 e steve at surrette.com
<http://www.facebook.com/RollsBattery>
<https://www.youtube.com/user/RollsBattery>
<https://www.youtube.com/RollsBatteryEngineering>
<https://www.youtube.com/RollsBatteryEngineering>
<https://www.youtube.com/RollsBatteryEngineering>
<https://www.linkedin.com/company/rolls-battery-engineering>
<https://www.linkedin.com/company/rolls-battery-engineering>
<https://www.linkedin.com/company/rolls-battery-engineering>
<http://www.instagram.com/RollsBattery>
<http://www.instagram.com/RollsBattery>
------------------------------
CONFIDENTIALITY: The information transmitted herein is intended only for
the addressee and may contain confidential, proprietary and/or privileged
material. Any unauthorized review, distribution or other use of or the
taking of any action in reliance upon this information is prohibited. If
you receive this email in error, please contact the sender and delete or
destroy this message and all copies.
------------------------------
On Wed, Jul 24, 2024 at 7:41 AM Drake Chamberlin via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> A severely abused bank of Rolls Surrette batteries had one battery off gas
> heavily on discharge. It seems like the off gassing happens on overcharge,
> not discharge. What could have caused that?
>
> Thank you,
>
> Drake
>
> Drake Chamberlin
> Athens Electric LLC
> Ohio Electrical Contractor’s License 44810
> NABCEP Certified PV Installation Professional
>
>
> --
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240724/6a875fcc/attachment.htm>
More information about the RE-wrenches
mailing list