[RE-wrenches] Another Mate 3 programming issues
Dave Angelini Offgrid Solar
offgridsolar at sti.net
Fri Jul 19 14:49:10 PDT 2024
MX60 was not networked which was the reason I stopped using them and
went to Xantrex around 2005. Not surprised that you could not change
MX60 settings on mate. Long time ago...
Dave Angelini Offgrid Solar
"we go where powerlines don't"
[2]https://offgridsolar1.com/ [3] [2]
e-mail offgridsolar at sti.net
text 209 813 0060
On 2024-07-19 9:59 am, Chris Schaefer via RE-wrenches wrote:
> Not sure if this helps but I had installed a full blown Outback twin
> VFX 3648 with two MX60's with the old green cabinets back in 2005. Last
> year I had to replace the two inverters with the new FXR as the VFX is
> discontinued. In order to do this I had to dump the old oval mate and
> move up to the Mate3s, as well as replace the old Hub 10.1 and use the
> newer 10.3. When all said and done, the Mate saw the old MX60's but you
> were unable to make changes or access any data/settings. One other
> note, the 2nd inverter goes on port 7 of the Hub, not port 2 as we've
> been use to in the past.
>
> Christopher
>
> On Fri, Jul 19, 2024 at 12:30 PM jay via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
> HI Chris,
>
> Can you give us more data?
>
> Like is this a new problem, or it only started after X?
>
> Since its not seeing the port ( NA) it could be the CC or the HUB, or
> the cable.
> the hub will show an active LED light if its connecting to anything on
> that port.
>
> You can try plugging into the CC directly to see if it reads it,
> probably easier with another mate.
>
> It just sucks to not have tech support or anyone on wrenches from some
> OEMS
>
> Jay
>
> On Jul 19, 2024, at 10:13 AM, Christopher Warfel via RE-wrenches
> <re-wrenches at lists.re-wrenches.org> wrote:
>
> This is grid tied system with all firmware updates that the Mate 3s
> recognizes. I cannot figure this blank data menu out. I have to
> program the battery ABS, FLOAT settings from the FM60 CC. System is 12
> years old so no Tech support available even if they answer the
> phone....
>
> Has anyone have advice for if this is normal, or if there seems to be
> an issue? Used a spare Mate 3s with no difference. Thank you, Chris
>
> --
> Christopher Warfel
> ENTECH Engineering Inc.
> PO Box 871, Block Island, RI 02807
> 401-477-5773
> <EEIlogolong.jpg> [1]
>
> <Mate3s Battery Setpoint
> Menu.jpg><cwarfel.vcf>_______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
--
Chris Schaefer's
Tel 585-229-2083 or Cell 585-748-1870
5115 S Hill Road ~ Canandaigua New York 14424
_www.solarandwindfx.com [4] ~ E-mail: chris at solarandwindfx.com_
Thomas Jefferson, the author of our great Constitution, once said,
"democracy" will cease to exist when you take away from those who are
willing to work and give to those who would not."
_______________________________________________
List sponsored by Redwood Alliance
Pay optional member dues here: http://re-wrenches.org
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
There are two list archives for searching. When one doesn't work, try
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
http://www.members.re-wrenches.org
Links:
------
[1] https://entech-engineering.com/Home/default.php
[2] http://members.sti.net/offgridsolar/
[3] https://offgridsolar1.com/
[4] http://www.solarandwindfx.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240719/191b7f8a/attachment.htm>
More information about the RE-wrenches
mailing list