I'm wondering if there are any precautions if charging a Fortress Evault
LFP bank using 1 or more OB charge controllers, in tandem with an Envy
inverter PV input.
I know it will have to be programmed differently, and it will be open loop,
no CC control from the BMU,.
This is a net metered system using a Fortress 12 kw inverter. The total PV
input of the inverter is 21 kw. Max sell back is 12 kw, while charging
batteries at 6 kw.
My issue is the customer has his heart set on maxing out the roof capacity
at 25 kw. And I don't really need to add a second inverter for
critical loads, Only to increase integrated DC-coupled PV capacity.
So I feasibly put part of the array on external charge controller(s) ,
open-looped, and the remainder on a single 12kw Envy inverter.
A second inverter also increases the AC capacity, and as a result, involves
a more comprehensive review for net metering approval in Vermont (new
trigger for additional review is greater than 15 kw AC)..
--