[RE-wrenches] Sol-Ark 15k solar panel frame grounding

Maverick Brown maverick at mavericksolar.com
Wed Jun 5 06:26:11 PDT 2024


I usually get the 08 GFDI error when I haven’t bonded neutral to ground downstream. (Typically because I booted up the inverter after DC connection but before any AC wires are landed.) That goes away once it is fully commissioned. 

I get the F23 - Tz_GFCI_OC_Fault If is related to the PV array, leakage or bonding. 

I do always run a properly sized ground wire from the array to the inverter ground. 

Thank you,

Maverick

Maverick Brown
Off-Grid Solar Commander since 2006
Maverick Solar Enterprises, Inc.
 • Solar Commander Remote Power
 • SunFlow Systems Cathodic Protection 
maverick at mavericksolar.com
512-460-9825



> On Jun 5, 2024, at 8:03 AM, Jason Szumlanski via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
> 
> Can anybody clarify the following instruction from the manual?
> 
> "GND the panel MOUNTS/FRAMES to any GND outside the circuit via 12AWG wire"
> 
> Does this mean do not connect the array equipment grounding conductor to the grounding terminal in the inverter? Where would be the suggested place to connect the equipment grounding conductor, and why does it make a difference? It would still be electrically bonded to the grounding terminal in the inverter. 
> 
> I'm asking because I do, in fact, have an equipment grounding conductor from the array connected to the ground terminal in the inverter at a home. I am getting an F08 GFDI fault. The manual doesn't say anything about the DC side with respect to this error. It suggests it is an AC current leakage to ground. But Sol-Ark tech support suggested that I disconnect the PV to rule it out as a source of the fault.
> 
> 
> 
> Jason Szumlanski 
> Florida Solar Design Group 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240605/f0f7b9bd/attachment.htm>


More information about the RE-wrenches mailing list