[RE-wrenches] 120 Vac and 12Vdc mixed distribution system
david quattro
david at quattrosolar.com
Fri May 3 17:03:59 PDT 2024
Might only be available for Latin American markets, I don’t know. Page 16
https://www.sol-ark.com/wp-content/uploads/Sol-Ark_ProductCatalog.pdf
On Fri, May 3, 2024 at 4:50 PM Jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Maybe the new 5kw 120v unit is the 8kw at 120v?
>
> Jay
>
> On May 3, 2024, at 4:22 PM, Tom McCalmont via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> David is correct. We have some experience with Sol-Ark’s inverter, and
> it’s a good product. However, be aware that you can configure it either as
> a 120V inverter with a max. output of about 5 kW or as a 240V inverter with
> a max. output of about 8 kW. However, it does NOT do split-phase, meaning
> if you configure it for 240V, it cannot run loads that require a neutral.
>
>
> Tom McCalmont
> Paired Power
>
>
> On May 3, 2024, at 4:12 PM, david quattro via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
> I think SolArk makes an 8K 120V-only version
> David
>
>
>
>
> On Fri, May 3, 2024 at 3:13 PM Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> For this application I was originally thinking about a 48V inverter with
>> 120V output, but there are not many options in the size range I was
>> considering. It hit me that I could potentially get a 120/240V split-phase
>> inverter and run the DC converter from one leg and the 120V loads from the
>> other leg. The Sol-Ark 8K would probably be the right size for this
>> application. Despite there being no 240V loads, they "could" add them in
>> the future if needed. I know about imbalance issues with the 12k, but have
>> not heard this same feedback about the 8k, so please let me know if you
>> know otherwise.
>>
>> I really doubt there will be enough imbalance here to cause issues. The
>> biggest load on the DC side is a tiny 12V DC pump and the largest load on
>> the AC side will be the new refrigerator, or maybe a big ceiling fan
>> starting up. The inductive loads are almost negligible. Really the only
>> reason I want an inverter this large is for the charger capacity. The owner
>> wants a 9.6kWh LiPo battery minimum, so I want a sizable charger.
>>
>> BUT, the client would need to replace their 120V portable generator with
>> a split-phase unit. That could be a sticking point taking me back to a 120V
>> inverter.
>>
>> I was hoping for an all-in-one for this particular job, but the only one
>> I can find that is 48Vdc and 120Vac is the EG4 6500EX-48. At the price
>> point they offer it, I guess it can't hurt to try! I can even have a spare
>> on the shelf for less in total than the cost of a Victron inverter charger
>> and separate charge controller, and still have money to spare. I have been
>> dabbling into the EG4 brand, mostly with clients that went ahead and bought
>> EG4 batteries before they ever met me, and I haven't had any real issues
>> other than battery to inverter closed loop comms. It's too early to say I'm
>> impressed, but the prices are in the too-good-to-be-true category. I don't
>> want to get off topic here with batteries and manufacturer reliability, but
>> I wanted to mention the EG4 6500EX-48, which seems like perfect specs for
>> this job.
>>
>>
>> And... I know... someone is probably thinking that we're up to a 9.6kWh
>> battery with a small 120V generator, and that's probably not a good match.
>> I get that, but the client expects the PV to handle all of their needs with
>> the generator only serving as an emergency backup. I have alerted them to
>> the potential mismatch. I still want a sizeable charger in case they
>> upgrade their generator for faster battery recharges.
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>> On Wed, Apr 24, 2024 at 1:52 PM John Blittersdorf via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Jason,
>>> Just using the converter works fine. They are considered a battery
>>> charger or a regulated power supply. I am currently running that way now
>>> with the battery cables going nowhere. I was thinking of putting the
>>> battery back in the system just for triple redundancy when my inverter hits
>>> low battery cutoff voltage on a cold winter night and no fuel for the
>>> generator (or it won't start).
>>> My Iota DLS puts out a regulated 13.4 volts up to 30 amps.
>>>
>>> John
>>>
>>> On Wed, Apr 24, 2024 at 8:25 AM Jason Szumlanski via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> Ah ha! I didn't consider using a small 12V battery with a charger. I
>>>> was thinking of just using a 120V -> 12V converter to handle the DC loads.
>>>> Is the 12V battery really necessary, or can I just power the DC loads
>>>> directly with a converter? If I just have lights and fans on the DC system,
>>>> the load should be pretty minimal.
>>>>
>>>> I could use a separate 12V battery, but I would like to eliminate that
>>>> cost and complexity if possible.
>>>>
>>>>
>>>> And yeah, I am not considering this a money making opportunity. It's
>>>> really just a challenge to ward off boredom from the daily grind.
>>>>
>>>
>>>> Jason Szumlanski
>>>> Principal Solar Designer | Florida Solar Design Group
>>>> NABCEP Certified Solar Professional (PVIP)
>>>> Florida State Certified Solar Contractor CVC56956
>>>> Florida Certified Electrical Contractor EC13013208
>>>>
>>>>
>>>> On Wed, Apr 24, 2024 at 8:01 AM John Blittersdorf via RE-wrenches <
>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>
>>>>> Jason,
>>>>> I have a customer with the same situation except he already has a 12
>>>>> V VFX inverter, He has a sunfrost fridge and other small loads with a very
>>>>> fancy custom control board
>>>>> originally set up to handle AC and DC systems. We are adding a lot
>>>>> more solar and I was considering a dual battery system but the owner didn't
>>>>> like that idea. We are going with and Iota 12v power supply (i use one at
>>>>> my house for my sunfrost) to power up all his DC loads and will be adding a
>>>>> large 48 V battery bank and over 4Kw of solar using a VFXR3648 directly in
>>>>> place of the 12V inverter. He complained that the existing inverter would
>>>>> not handle all his current AC loads very well. My own house is fully wired
>>>>> for 12VDC as well as AC (lots of #10 copper not being used) and I have been
>>>>> considering getting a small LFP 12V battery to put back on by DC System.
>>>>> Then use the Iota as a secondary charging method with some of my large
>>>>> stash of older modules hooked up for 12V direct with C40 charge controller
>>>>> to recreate my original system just for kicks. I'm only using DC for my
>>>>> Sunfrost and one "emergency light" in the livingroom right now. For your
>>>>> customer, a small LFP 12v battery (approximately $500 or less) to replace
>>>>> his old battery bankm and more larger ones for the new AC side with 48V
>>>>> inverter fed by his generator or through an Iota 48 V charger ifusing a
>>>>> smaller non charging inverter. Unlike Dave, I like these challenges. Maybe
>>>>> thats why I never seem to make money.!!
>>>>>
>>>>> John Blittersdorf
>>>>> offgridvermont.com
>>>>>
>>>>>
>>>>> On Wed, Apr 24, 2024 at 7:22 AM Jason Szumlanski via RE-wrenches <
>>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>>
>>>>>> Fortunately, the owner is pretty handy and is willing to live with
>>>>>> any negative consequences. That said, I want to offer him something as
>>>>>> simple and bulletproof as possible. I am walking into this with eyes wide
>>>>>> open, for sure.
>>>>>>
>>>>>> Jason Szumlanski
>>>>>> Principal Solar Designer | Florida Solar Design Group
>>>>>> NABCEP Certified Solar Professional (PVIP)
>>>>>> Florida State Certified Solar Contractor CVC56956
>>>>>> Florida Certified Electrical Contractor EC13013208
>>>>>>
>>>>>>
>>>>>> On Tue, Apr 23, 2024 at 5:47 PM Dave Angelini Offgrid Solar via
>>>>>> RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>>>>>>
>>>>>>> Not being helpful but I walk away from these. It will come back to you.
>>>>>>>
>>>>>>> *Dave Angelini Offgrid Solar
>>>>>>> "we go where powerlines don't"
>>>>>>> <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>
>>>>>>> e-mail offgridsolar at sti.net <offgridsolar at sti.net>
>>>>>>> text 209 813 0060*
>>>>>>>
>>>>>>>
>>>>>>> On 2024-04-23 2:40 pm, Jason Szumlanski via RE-wrenches wrote:
>>>>>>>
>>>>>>> I have an off-grid client who is working on replacing old equipment
>>>>>>> at a cabin. He has a lot of 12 volt distribution in the house for lighting,
>>>>>>> fans, and a 12 volt refrigerator. He also has 120 volt AC loads that run
>>>>>>> through a separate distribution panel where the only source is a 2000 Watt
>>>>>>> Honda generator. There is no inverter present. The batteries are charged
>>>>>>> through a Trace C40.
>>>>>>>
>>>>>>> He currently has a few ancient solar panels and a struggling Bank of
>>>>>>> AGM batteries. It's time for an upgrade. I can easily supply enough PV
>>>>>>> power for what he needs. He currently has a 9 kilowatt hour battery
>>>>>>> capacity that he was happy with when the batteries operated optimally.
>>>>>>> Nonetheless, I would probably future-proof him with a 10 to 15 kilowatt
>>>>>>> hour LiPo to double or triple his usable capacity.
>>>>>>>
>>>>>>> For convenience, obviously it would be nice to have an inverter to
>>>>>>> eliminate or reduce the generator requirement. But he seems committed to
>>>>>>> keeping his 12 volt distribution because it would be costly to replace
>>>>>>> fixtures. I think he would consider replacing the 12 volt refrigerator if
>>>>>>> he has an inverter.
>>>>>>>
>>>>>>> He definitely wants LiPo batteries.
>>>>>>>
>>>>>>> I don't like the idea of 12 volt direct from a battery plus
>>>>>>> connecting an inverter to that same battery. It is going to be hard to
>>>>>>> measure and monitor things.
>>>>>>>
>>>>>>> I am thinking about using a 48 volt battery with a single phase 120
>>>>>>> volt inverter, getting him to change to a 120 volt refrigerator, and using
>>>>>>> a DC converter to give him somewhere in the range of 100 amps at 12 volts
>>>>>>> for his existing DC lighting and fan loads. Is this a bad idea? Should I
>>>>>>> stick with a 12 volt battery system? He does have a tiny 12 volt pressure
>>>>>>> pump which might be an issue for the converter. I'm not sure. I am a bit
>>>>>>> worried about the efficiency loss and capacity of DC converters and not
>>>>>>> sure how to size it.
>>>>>>>
>>>>>>> Jason Szumlanski
>>>>>>> Florida Solar Design Group
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>>
>>>>>>> _______________________________________________
>>>>>>> List sponsored by Redwood Alliance
>>>>>>>
>>>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>>>
>>>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>>
>>>>>>> Change listserver email address & settings:
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>>
>>>>>>> There are two list archives for searching. When one doesn't work,
>>>>>>> try the other:
>>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>>
>>>>>>> List rules & etiquette:
>>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>>
>>>>>>> Check out or update participant bios:
>>>>>>> http://www.members.re-wrenches.org
>>>>>>>
>>>>>>> _______________________________________________
>>>>>>> List sponsored by Redwood Alliance
>>>>>>>
>>>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>>>
>>>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>>
>>>>>>> Change listserver email address & settings:
>>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>>
>>>>>>> There are two list archives for searching. When one doesn't work,
>>>>>>> try the other:
>>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>>
>>>>>>> List rules & etiquette:
>>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>>
>>>>>>> Check out or update participant bios:
>>>>>>> http://www.members.re-wrenches.org
>>>>>>>
>>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>>
>>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> There are two list archives for searching. When one doesn't work, try
>>>>>> the other:
>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org
>>>>>>
>>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240503/8ee3f664/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: image_6487327.JPG
Type: image/jpeg
Size: 209923 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240503/8ee3f664/attachment-0001.jpe>
More information about the RE-wrenches
mailing list