[RE-wrenches] 120 Vac and 12Vdc mixed distribution system
Darryl Thayer
darylsolar1 at gmail.com
Fri Apr 26 09:04:04 PDT 2024
I agree with John also. one of the better-performing off-grid houses I
worked on used a 48 to 12-V Samlex converter. The 12-volt thick-walled
refrigerator was about 4 amps at 12 volts. The lights, radio, and small TV
drew very few amps each/ I also used an Outback 3648 inverter, which the
homeowner turned on only. when needed (wash machine, etc.), I used SQ-D QO
panel board in case the owner wanted to go to 120 volt AC future breaker
panel. All lighting was Edison base lamps, and all wiring was NMB Romex. I
wired like a normal house except for a 120-v panel and 12-v panel I relay
and momentary switch by appliance for easy turning on of AC inverter.
On Wed, Apr 24, 2024 at 8:49 AM Jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> I agree with John.
>
> Most 12v fridges have small compressors. But I don’t know what they have.
> Personally a major reason to go 120/ac is to get a normal refrigerator.
>
> But you can measure the surge/load and then size the charger accordingly.
>
> One feature of going charger is the lights are a lot brighter at night and
> last longer because they are not at 15v during the day.
>
> Jay
>
>
> On Apr 24, 2024, at 5:01 AM, John Blittersdorf via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Jason,
> I have a customer with the same situation except he already has a 12 V
> VFX inverter, He has a sunfrost fridge and other small loads with a very
> fancy custom control board
> originally set up to handle AC and DC systems. We are adding a lot more
> solar and I was considering a dual battery system but the owner didn't like
> that idea. We are going with and Iota 12v power supply (i use one at my
> house for my sunfrost) to power up all his DC loads and will be adding a
> large 48 V battery bank and over 4Kw of solar using a VFXR3648 directly in
> place of the 12V inverter. He complained that the existing inverter would
> not handle all his current AC loads very well. My own house is fully wired
> for 12VDC as well as AC (lots of #10 copper not being used) and I have been
> considering getting a small LFP 12V battery to put back on by DC System.
> Then use the Iota as a secondary charging method with some of my large
> stash of older modules hooked up for 12V direct with C40 charge controller
> to recreate my original system just for kicks. I'm only using DC for my
> Sunfrost and one "emergency light" in the livingroom right now. For your
> customer, a small LFP 12v battery (approximately $500 or less) to replace
> his old battery bankm and more larger ones for the new AC side with 48V
> inverter fed by his generator or through an Iota 48 V charger ifusing a
> smaller non charging inverter. Unlike Dave, I like these challenges. Maybe
> thats why I never seem to make money.!!
>
> John Blittersdorf
> offgridvermont.com
>
>
> On Wed, Apr 24, 2024 at 7:22 AM Jason Szumlanski via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> Fortunately, the owner is pretty handy and is willing to live with any
>> negative consequences. That said, I want to offer him something as simple
>> and bulletproof as possible. I am walking into this with eyes wide open,
>> for sure.
>>
>> Jason Szumlanski
>> Principal Solar Designer | Florida Solar Design Group
>> NABCEP Certified Solar Professional (PVIP)
>> Florida State Certified Solar Contractor CVC56956
>> Florida Certified Electrical Contractor EC13013208
>>
>>
>> On Tue, Apr 23, 2024 at 5:47 PM Dave Angelini Offgrid Solar via
>> RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Not being helpful but I walk away from these. It will come back to you.
>>>
>>> *Dave Angelini Offgrid Solar
>>> "we go where powerlines don't"
>>> <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/> <http://members.sti.net/offgridsolar/>
>>> e-mail offgridsolar at sti.net <offgridsolar at sti.net>
>>> text 209 813 0060*
>>>
>>>
>>> On 2024-04-23 2:40 pm, Jason Szumlanski via RE-wrenches wrote:
>>>
>>> I have an off-grid client who is working on replacing old equipment at a
>>> cabin. He has a lot of 12 volt distribution in the house for lighting,
>>> fans, and a 12 volt refrigerator. He also has 120 volt AC loads that run
>>> through a separate distribution panel where the only source is a 2000 Watt
>>> Honda generator. There is no inverter present. The batteries are charged
>>> through a Trace C40.
>>>
>>> He currently has a few ancient solar panels and a struggling Bank of AGM
>>> batteries. It's time for an upgrade. I can easily supply enough PV power
>>> for what he needs. He currently has a 9 kilowatt hour battery capacity that
>>> he was happy with when the batteries operated optimally. Nonetheless, I
>>> would probably future-proof him with a 10 to 15 kilowatt hour LiPo to
>>> double or triple his usable capacity.
>>>
>>> For convenience, obviously it would be nice to have an inverter to
>>> eliminate or reduce the generator requirement. But he seems committed to
>>> keeping his 12 volt distribution because it would be costly to replace
>>> fixtures. I think he would consider replacing the 12 volt refrigerator if
>>> he has an inverter.
>>>
>>> He definitely wants LiPo batteries.
>>>
>>> I don't like the idea of 12 volt direct from a battery plus connecting
>>> an inverter to that same battery. It is going to be hard to measure and
>>> monitor things.
>>>
>>> I am thinking about using a 48 volt battery with a single phase 120 volt
>>> inverter, getting him to change to a 120 volt refrigerator, and using a DC
>>> converter to give him somewhere in the range of 100 amps at 12 volts for
>>> his existing DC lighting and fan loads. Is this a bad idea? Should I stick
>>> with a 12 volt battery system? He does have a tiny 12 volt pressure pump
>>> which might be an issue for the converter. I'm not sure. I am a bit worried
>>> about the efficiency loss and capacity of DC converters and not sure how to
>>> size it.
>>>
>>> Jason Szumlanski
>>> Florida Solar Design Group
>>>
>>>
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240426/55f12759/attachment.htm>
More information about the RE-wrenches
mailing list