[RE-wrenches] Redundant gensets: Must I switch the neutral in the manual transfer switch?
Kent
kent at coveoregon.com
Wed Mar 13 16:01:41 PDT 2024
First, I'll say that I agree with William's discussion. Let me add
another way of thinking about this:
Assume that, instead on two generators, your system is one backup
generator and one utility company serving a commercial building. If the
disconnect switch is your service connection, there will be a N-G bond
located there and none will be allowed in the generator.
Kent Osterberg
Blue Mountain Solar
On 3/13/2024 2:19 PM, Mick Abraham via RE-wrenches wrote:
> Hi, Mechanix~
>
> My off grid project gig has redundant 120y208 generators that need a
> 200a "break before make" manual transfer switch so the clients can
> choose machine A or machine B. The switch has a lockable center-off
> but I think the generators aren't set up for "lock out tag out". The
> machines & the xfer switch will all be indoors and about 10 feet
> apart. The AC power wires from each generator will be hard-wired to
> the transfer switch & piped in EMT. I had planned for the transfer
> switch to have a "solid neutral" bus bar (& I had planned to bond
> Neutral to Ground in that box), but a consulting EE tells me the
> neutral must be switched along with the three hots. The project is too
> remote to have an AHJ, but the clients have requested a wet stamp from
> the EE.
>
> I think his rationale is related to the N-G bond point location. When
> I asked about his suggested location, the EE wrote: "The N-G bond will
> be at each generator, so the neutral will be generated at the
> generator providing power to the facilities."
>
> Mick resumes: The genset installation document says "The generator set
> is shipped from the factory with the neutral and equipment ground not
> bonded together." So...these gensets are not like those portables
> where it's difficult to isolate the neutral. I've attached an image
> that shows what the EE is advocating. The manual xfer switch that I
> wish to use isn't made in "four poles" without going to the 400 amp
> version and the 400a switch won't physically fit the available space.
>
> Can I make a credible case for the transfer switch being the "point of
> first disconnect" instead of each generator taking turns at being the
> POFD? If the transfer switch is also the bond point, can't the Neutral
> from each generator happily meet at the neutral bus bar? OR: might the
> EE have a concern about a loop (from the Neutral of one genset through
> the bus bar then showing up on the terminal strip for the other
> genset? Code citations would be appreciated along with your advice,
> Wrenchies.
>
> During service intervals, both engines will be running for a
> brief interval. Example: Gen A may be carrying the loads while the
> mechanic manually runs Gen B as he completes an oil change. If I wire
> it as the EE wishes, will both running machines play well safety-wise
> if each genset has a N-G bond (with the equipment ground as their only
> common connection)? How would the safety aspects change if both
> machines are running but I've wired things per my original concept?
>
> Thanks as always, Mechanix. "The Wrench List is the Bomb!"
>
> Mick Abraham, Proprietor
> www.abrahamsolar.com <http://www.abrahamsolar.com>
>
> Landline: 970-731-4675
> Cell phone or for text messaging: 970-946-6584