[RE-wrenches] Tigo RSS Off Grid
Bradley Bassett
bbassett2 at gmail.com
Sat Feb 17 08:35:36 PST 2024
I powered a MidNite LSOB transmitter from a Classic AUX, though the
receivers didn't work with the Classic. The Classic is limited to 200ma
output and the Tigo and APS transmitters are rated at up to 800ma input, so
it might overload the Classic AUX output if they really do draw that much.
I tested an APS RSD system recently with a Classic and it did not work
well. I believe that the Tigo transmitter is very similar since the APS
devices say "licensed by Tigo" on them, So, the Tigo RSD devices may not
work well with a Classic either.
What I recommended while at AEE was to use a 48VDC to 12VDC converter to
power the Tigo and APS transmitters. This works well. Here's the one I
recommended if it's still available: mean-well/ddr30l12
<https://www.onlinecomponents.com/mean-well/ddr30l12-50161036.html> I
never had any negative feedback using this with a Sol-Ark and APS devices.
With a Classic in the system I've had to use the FireRaptor RSD devices. If
you can get approval or have older modules, you might be able to follow the
FireRaptor instructions and use 2 modules in series for each FireRaptor.
You do still have to have a way to disconnect the PV output circuit from
the Classic in order to make that circuit dead from the Classic end of the
circuit. I did that by putting an MNPV6-disco on the power shed which
disconnects the PV output circuit as well as the 24VDC to the FireRaptors.
And, I am powering my FireRaptors at 15VDC and it works fine.
Brad Bassett, ret.
On Fri, Feb 16, 2024 at 6:47 PM Jeremy Rodriguez via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Has anyone successfully used a MidNite Classic CC to power a Tigo Rapid
> Shutdown Transmitter in an off grid setting ? Specifically using the 12v
> Aux output to keep the PV circuits alive instead of relying on the inverter
> AC output to do this.
>
> Think of this scenario. Batteries reach LBCO, inverter shuts OFF, no PV
> to re charge back to LBCI, no generator backup to recharge batteries.
>
>
> Jeremy Rodriguez
> Solar Installation / Design
> All Solar, Inc.
> 1453 M St.
> Penrose Colorado 81240
>
> Sent by Jeremy's iPhone. Sorry for typos and shorthand.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240217/6f463021/attachment.htm>
More information about the RE-wrenches
mailing list