I've used Midnite DC combiners in the past with good results. Since you are
over 150 VDC, I believe you'd need to select the 1000 VDC fuse holder(s)
for your application:

https://www.midnitesolar.com/productPhoto.php?product_ID=78&productCat_ID=9&sortOrder=4&act=p

August


On Thu, Jan 18, 2024 at 7:43 AM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:

> I am installing an EG4 off-grid 3k inverter for the first time, and the
> manual requires a DC circuit breaker on the PV input. It will be a small PV
> array with adjusted max Voc around 280V @ Isc 10.6A.
>
> I'm looking for a cost-effective DC breaker and enclosure for this purpose.
>
> Jason Szumlanski
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida Certified Solar Contractor CVC56956
> Florida Certified Electrical Contractor EC13013208
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20240118/b49291b1/attachment.htm>


More information about the RE-wrenches mailing list