[RE-wrenches] SMA TL-22 insulation resistance error

drake.chamberlin at redwoodalliance.org drake.chamberlin at redwoodalliance.org
Wed Dec 13 08:01:16 PST 2023


It could be the inverter. The TL-22 series had a lot of problems with
false arc fault errors.  

_Drake Chamberlin_ 

_Athens Electric LLC_ 

_Ohio Electrical Contractor's License 44810_ 

_NABCEP Certified PV Installation Professional_

---

On 2023-12-13 10:52, Dave Tedeyan via RE-wrenches wrote:

> Hi All, 
> 
> I am curious to hear if anyone else has run into this: 
> 
> This is the system I posted about a little while ago that had the SolarWorld modules and all the module to module connectors were swollen and melted. One of the inverters was giving an insulation resistance error, and so after seeing the module connectors, I was sure that was the issue. We replaced every single module connector with new MC4's, and then the error came back! 
> 
> My next step was to swap in the junction box which strings go to which inverter to identify whether the issue was on the roof or somewhere between the roof jbox and the inverter. (the issue was isolated to only 1 of 4 strings previously). Turns out the same inverter is faulting, which leads me to believe that there may be an issue with the wires in the DC conduit. Maybe they got damaged by a rough wire pull at the initial installation 7 years ago, and its finally degraded enough to cause a problem. The fault is intermittent, only showing up once every couple weeks or so, so it is difficult to catch it while the fault is active.  
> 
> But my question is, could there also be something wrong with the inverter itself? After spending a lot of time on this one, ideally, I would know that replacing the DC wires will fix it. So I am curious if people have done this, to still find that the issue was something internal to the inverter. 
> 
> Thanks! 
> -Dave
> -- 
> 
> [1]
> 
> Dave Tedeyan, P.E.
> Owner | Sungineer Solar
> 
> p: he | him | his
> a: 1653 Slaterville Rd. | Ithaca, NY 14850
> w: www.sungineersolar.com [2]
> c: (607) 270-0370 
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
 

Links:
------
[1] https://www.sungineersolar.com/
[2] http://www.sungineersolar.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20231213/64bad3fc/attachment.htm>


More information about the RE-wrenches mailing list