[RE-wrenches] Cable sizing for high current modules? NEC interpretation/guidance?
Bradley Bassett
bbassett2 at gmail.com
Wed Nov 8 09:13:30 PST 2023
Hi George, It's good to see you're still with REC.
I'd assume this would fall under the purview of UL rather than NEC.
Anything that meets UL will pass NEC. With temperature derates I think
you'd have had to go to larger wire long ago to meet NEC standards.
It might be good to go to a larger wire to keep V drop low.
Brad Bassett
retired, but still interested.
On Wed, Nov 8, 2023 at 9:07 AM George McClellan via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Team;
>
>
>
> With the move to larger cells, some modules have an Isc that is pushing
> the limits of 12 AWG wire. If I apply the rule of 156% (or 125% solar
> derate*125% continuous load derate) to an 18 Amp Isc module this will
> exceed the 25A that a 12 AWG wire can carry. I understand that the
> homeruns will need to be a larger AWG (10 ga), but do the solar module
> cables (from junction box to MC4) also need to be larger? Any guidance or
> reference material would be greatly appreciated.
>
>
>
> Thx,
>
>
>
> George McClellan | Senior Technical Sales Manager | REC Americas LLC
>
> 330 James Way Ste 150 | Pismo Beach, CA 93449 | USA
>
> Cell phone +1 805 704 3226 | Fax +1 805 357 6104
>
> www.recgroup.com | george.mcclellan at recgroup.com
> <shannon.kent at recgroup.com>
>
>
>
> ------------------------------
>
> This message is private and confidential and may be privileged. Any
> unauthorized use, dissemination of the information or copying of this
> message is prohibited. If you have received this message in error, please
> notify us immediately and remove it from your system. Thank you.
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20231108/8a996486/attachment.htm>
More information about the RE-wrenches
mailing list