[RE-wrenches] AC Coupling

Dave Angelini Offgrid Solar offgridsolar at sti.net
Mon Oct 30 09:41:57 PDT 2023



 From Schneider, who leads in it all the way back to Trace Engineering. 
The interlock is to protect the genset from backfeed. Sometimes a block 
diagram can help.

A link to their guide which explains the history back to Legacy grid tie 
inverters.

https://www.solar-electric.com/lib/wind-sun/Conext-XW-Pro-SW-AC-Coupling-Guide.pdf

Dave Angelini Offgrid Solar
"we go where powerlines don't"
    [9]https://offgridsolar1.com/ [10]  [9]
e-mail  offgridsolar at sti.net
text 209 813 0060

On 2023-10-30 9:14 am, Steve Higgins via RE-wrenches wrote:

> Good Morning Wrenches,
> 
> AC-coupled systems are generally not pleasant to batteries of any type. 
>  I would not AC Couple any Valve Regulated Battery system as you are, 
> in essence, "overcharging" them at times, and this can and has led to 
> battery failures (usually overcharging and swelling) that all battery 
> manufacturers will not cover under warranty.    Flooded batteries can 
> take this abuse a bit more, but this can still result in drying the 
> batteries out and corrosion or degradation of the negative plate due to 
> heat.
> 
> Lithium batteries do not like this, but the BMS will shut off the 
> charge to the battery bank. It doesn't power off the battery but stops 
> the excessive charge to the battery, but these unloaded voltages on the 
> input of the battery can stress the BMS depending on how much voltage 
> is seen.
> 
> Ideally, if you are AC coupling, it's better to use a system that 
> tapers charging and voltage depending on SOC, to do this you'll need 
> closed loop communication, with the inverter/charger so the battery can 
> shut down or slow charging depending on SOC.
> 
> [1]
> Steve Higgins ⋅ Technical Services Manager
> t +1.902.597.4020  m +1.206.790.5840
> f +1.902.597.8447  e steve at surrette.com
> [2] [3] [4] [5]
> 
> -------------------------
> 
> CONFIDENTIALITY: The information transmitted herein is intended only 
> for the addressee and may contain confidential, proprietary and/or 
> privileged material. Any unauthorized review, distribution or other use 
> of or the taking of any action in reliance upon this information is 
> prohibited. If you receive this email in error, please contact the 
> sender and delete or destroy this message and all copies.
> -------------------------
> 
> On Mon, Oct 30, 2023 at 8:53 AM William Miller via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Jason:
> 
> Thanks for contributing to this thread.  I did not realize it would 
> create so much interest.  My main point is to establish a definition 
> for AC-coupling, and I believe we do have consensus on that.  The next 
> question to ask is AC-coupling a good thing?
> 
> You make the point that BMS systems protect lithium batteries from 
> damage.  They do so by shutting down, not correcting the problem.  But 
> what good is a system that shuts down?  When that happens someone has 
> to roll a truck to reset the system.  We should not design outages into 
> our systems.
> 
> I spoke at length this weekend with a very knowledgeable member of this 
> forum (thank you, sir) about closed loop.  Their experience is that 
> there were packet losses in the communications and when that occurred 
> the system shut down.  I am going to set up my first closed loop today 
> and I hope I do not have the same experience.
> 
> Traditional charge controllers may seem "crude" but they operate on 
> real, measured values of voltage and current, values that are at the 
> core of battery care.  Modern charging systems seem to rely at least 
> partially on sate of charge.  State of charge is a calculated value 
> that is notorious for being inaccurate and drifting more so over time.  
> Every SOC scheme I know needs to be recalibrated frequently.  The 
> recalibration requires hitting certain charge parameters and if you 
> can't hit those you don't recalibrate.
> 
> I assumed that a BMS system provided within a lithium battery assembly 
> by the manufacturer would be accurate.  I spoke with a tech support 
> person from a prominent LFP manufacturer at length recently and was 
> told their BMS is not foolproof on calculating SOC.  I am not confident 
> that any of them are.
> 
> I am new to lithium battery systems.  It may be my inexperience 
> talking, but it seems they incorporate a lot of complexity that may 
> make them unreliable unless charged and discharged very carefully.  I 
> do not believe AC-coupled charging is a good way to charge lithium 
> batteries, or any battery.
> 
> William Miller
> 
> Miller Solar
> 
> 17395 Oak Road, Atascadero, CA 93422
> 
> 805-438-5600
> 
> www.millersolar.com [6]
> 
> CA Lic. 773985
> 
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On 
> Behalf Of Jason Szumlanski via RE-wrenches
> Sent: Monday, October 30, 2023 7:33 AM
> To: RE-wrenches
> Cc: Jason Szumlanski
> Subject: Re: [RE-wrenches] AC Coupling
> 
> I read through this thread, and I don't think one important aspect was 
> covered with respect to "overcharging" batteries. There may be risk 
> with lead acid batteries connected to a hybrid inverter that is AC 
> coupled. But LiPO batteries have a BMS that is there, in part, to 
> protect the battery from an overcharge scenario. The BMS is going to 
> disconnect the battery before catastrophe strikes. In my opinion, AC 
> Coupling is better suited to modern equipment that talks to each other 
> in a closed loop. Crude algorithms for throttling PV don't seem 
> particularly confidence-inspiring. This is one argument for sticking 
> with a single manufacturer system architecture (i.e. Enphase). While 
> there are obvious downsides and limitations to that, the system should 
> work safely and flawlessly in an AC Coupled scenario.
> 
> With respect to mixed systems with DC and AC Coupling, while I see the 
> advantages, it really complicates the design and installation. It also 
> greatly confuses the monitoring aspect for PV production. I think it 
> depends on the scenario, but going one way or the other makes the most 
> sense to me in most situations. With that said, there are exceptions. 
> For example, I have a Sol-Ark 15K client right now where all of the 
> MPPT inputs are taken, and reconfiguring the DC coupled strings is not 
> easily achieved. So, to add more PV, the obvious choice is to AC 
> couple. But this system has a generator, so the AC Coupled PV needs to 
> be on the AC load output, meaning it will not be monitored by the 
> Sol-Ark. That's not ideal, but it's nice to have that flexibility.
> 
> Jason Szumlanski
> 
> Principal Solar Designer | Florida Solar Design Group
> NABCEP Certified Solar Professional (PVIP)
> Florida State Certified Solar Contractor CVC56956
> 
> On Sun, Oct 29, 2023 at 4:19 PM Kienan Maxfield via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> William,
> 
> My whole email is in regards to the point you made when you said
> 
> "This is not how battery inverters were originally designed to operate. 
>  These systems require careful consideration to avoid battery 
> overcharging."
> 
> I both agree and disagree with these statements... depending on what 
> you mean. I don't think it's super helpful to say that careful 
> considerations are required without mentioning what those 
> considerations are, and I'll get to those below.
> 
> When you say that the battery inverters "weren't originally designed 
> for this" I'd agree to an extent.. The "original" battery based 
> inverters 25 years ago were certainly not designed for AC coupling. 
> They weren't "originally" designed for it. But that was then and this 
> is now.
> 
> Now William is correct that the Gen input becomes an AC output, and you 
> can't wire the gen into that "input" if you are using it as a PV 
> input... that being said, Jay didn't think otherwise, he was just 
> critiquing the wiring diagram in the original post to say that it wires 
> up differently, so I'd say that you are both right on this one. That 
> said, I don't think anyone says you have to wire it into the gen port, 
> I think that even with the hybrid inverters, the way in William's 
> original post is still a fully acceptable way to do it.
> 
> I am not a huge fan of AC coupling, however, I have done it a fair 
> amount and I have a fair amount of experience with it off-grid with 
> Lithium and with Lead Acid. Most of my experience is with Outback and 
> Victron, but I have some experience with Schneider as well. These 
> systems have been working really well for a good while, but that being 
> said, Schneider had some real problems at first (major headache).
> 
> Now when it comes to hybrid inverters, I'm still not a huge fan... but 
> I'm starting to try them out. I have not tested AC coupling with any of 
> them yet. I was at a conference less than a year ago and one of the 
> major brands was saying that there is no hybrid inverter that supports 
> both AC coupled PV and a generator at the same time for a grid tied 
> system. They said "you can't have it all." There may be an exception to 
> that, I've never looked into it, but with the Victron and Outback (and 
> probably Scheider... IDK) it's easy to have it all. I've done it and it 
> works well in every mode. The frequency changes super fast and assuming 
> you have a properly programmed rule 21 compliant Grid tied inverter, it 
> responds very quickly, and in the systems I've monitored, the frequency 
> never had to go above 62 Hz, which is good enough for most sensitive 
> loads. The inverters are totally designed for this these days, but if 
> you have highly sensitive loads, then it may not work well.
> 
> Considerations...
> 
> First of all, I will be assuming that you are using quality rule 21 
> grid-direct inverters and a good battery inverter that works as well as 
> the Outback Radian or the Victron. The early Schneiders were too slow 
> in changing their frequency, and special considerations had to be 
> accounted for because of that, but I heard that was fixed a while ago. 
> You had to reduce the charging voltages to account for the delayed 
> throttling, but I can attest that even in the early days, Outback never 
> had this problem, and Victron works smoothly as well.
> 
> The primary problem for AC coupling is in off-grid scenarios or 
> prolonged power outages, and that's the black start issue (or dark 
> start). Simply put, if your battery gets low and the battery inverter 
> turns off, then your PV can't charge the battery. This problem is 
> lessened when you connect the PV Grid Direct inverters to a dedicated 
> output on the inverter so that the loads shut down while the battery is 
> still a few percent above the inverter shutdown level. That is a nice 
> advantage of the Victron inverters. I don't know if the Hybrid 
> inverters do this or not. In any case, even with this little safety 
> net, the inverter can still discharge the battery to the point where 
> the inverter turns off and you have a problem. My solution is that you 
> should have at least a little bit of the PV DC coupled so that when the 
> sun comes out, the voltage will rise and the inverter will turn on. 
> This is also recommended in Victron's AC Coupling manual.
> 
> The second consideration is the minimum inverter size... Your battery 
> based inverter needs to be capable of handling and controlling the full 
> PV power. Victron recommends that the maximum PV power (DC or AC, 
> whichever is lower) does not exceed 100% of the rating of the inverter 
> (no more than 10kW of power from the PV on a 10kW inverter). Outback 
> recommends no more than 6 kW of Grid-Tied inverter per 8 kW of Radian 
> (so that's 75% of the battery inverter's power). In some circumstances, 
> this could demand upsizing the battery inverter, which is another great 
> reason to DC couple half of the PV and AC couple the other half... 
> because then you could effectively have more PV with less battery based 
> inverter, depending on your loads.
> 
> As was mentioned by William, monitoring is generally not as good with 
> an AC coupled system, but here again, that's not always true. Victron 
> has been really leading the way with integrating with other PV 
> grid-tied inverters so that you can monitor them through Victron's own 
> monitoring. This depends on the brand you are connecting to, but most 
> of these brands have a way to get this information via TCP/IP, and if 
> so, Victron will read that and report it on their own website, in their 
> app, and on their touchscreen. With some brands, you can even see the 
> error codes etc. remotely through Victron's monitoring. It almost makes 
> it seamless as though it was all one brand.
> 
> So in case it's not clear, I'm never a fan of 100% AC coupled PV, but 
> these days there are very few legitimate concerns or issues... Most if 
> not all of which disappear with a 10% - 60% DC coupled system.
> 
> Thanks,
> 
> Kienan
> 
> Green-Go Solar Wholesale Distribution
> 
> maxfieldsolar at hotmail.com
> 
> (801) 631-5584 (Cell)
> 
> www.distribution.solar
> 
> -------------------------
> 
> From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on behalf 
> of Jerry Shafer via RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Sent: Saturday, October 28, 2023 11:14 PM
> To: William Miller <william at millersolar.com>; RE-wrenches 
> <re-wrenches at lists.re-wrenches.org>
> Cc: Jerry Shafer <jerrysgarage01 at gmail.com>
> Subject: Re: [RE-wrenches] AC Coupling
> 
> AC coupled systems used to work like this but with solark and sort of 
> with outback they use the gen set input to the inverter, do the freq 
> shift and charge via a preset voltage. This seams to work well but if 
> you connect a genny it must be on the grid input via an ATS, alot more 
> complicated the any DC side connection.
> 
> Funtimes
> 
> On Sat, Oct 28, 2023, 8:51 PM William Miller via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Jay:
> 
> I am not sure how it would be possible for a grid-tied inverter to 
> operate with any battery inverter if it was not connected to the 
> battery inverter AC output.  The grid-tied inverter needs to see 
> correct voltage and frequency before it can start up.  How else could 
> this work?
> 
> I looked up all of the inverters you cited.  In each case it may look 
> to you like you are connecting to an input, it is really just 
> reprogramming the inverter to turn the generator input into an extra 
> output.  All of the manufacturers provide warnings about doing this.  
> Here is more information from each of the manufacturers:
> 
> Sol-arc:  From the manual for the Sol-arc 15K-2P-N: You convert the Gen 
> input to an output and make that your connection point.  "_A full AC 
> coupled solar system is not recommended as power control and monitoring 
> is limited."_
> 
> EG4:  I could not find an "ev4" inverter anywhere online.  There is an 
> EG4 inverter.  I read the manual and it looks like the EG4 works just 
> like the Sol-arc:  You program the generator input to actually be an 
> output.  The EG4 abruptly disconnects that output when battery SOC 
> reaches a programmed level-- There is apparently no frequency shift 
> function.  The manual is pretty inadequate on this point but they do 
> provide a video [7].
> 
> Fortress:  The same as above is true about using the generator input 
> for AC-coupling on the Fortress FP-Envy-12k.  From that manual_:  It is 
> forbidden to connect the Generator in Gen Port when AC Coupled.  _That 
> is because when AC-coupling, the generator input is no longer an input.
> 
> So while it appears one connects an AC-Coupled inverter to battery 
> inverter inputs, it is just a reprogramming of the generator input to 
> be an output.  In all cases that I can see there is still no voltage 
> control of AC-coupled battery charging.
> 
> I am aware that to try and provide some modicum of control over the 
> battery charging from AC-coupled sources, a scheme was invented to 
> shift the output frequency and taper or shut down AC-coupled power.  
> This is a work-around, not a design.  In each and every one of these 
> systems it is pretty clear there is little control over battery 
> charging voltage.  These systems do not support three stage battery 
> charging like a DC charge controller can.
> 
> When AC-coupled charging is connected to batteries with BMS in certain 
> conditions battery voltage spikes can occur.  See section 2.2 of this 
> article. [8]
> 
> There are limited advantages to AC coupling:
> 
> ·        AC coupling allows reduced wire gauge for long-haul feeders.  
> This is no longer as necessary with new 600 volt input charge 
> controllers.
> 
> ·        AC Coupling allows an easier upgrade path for a customer that 
> has grid-tied inverters and wants to add batteries.  I am not sure most 
> batteries can survive for long with the crude charging algorithm 
> provided, so I would hesitate to recommend this.
> 
> In my opinion AC-coupled battery charging with even the newest 
> inverters is a crude affair.  I am not a fan.
> 
> William
> 
> Miller Solar
> 
> 17395 Oak Road, Atascadero, CA 93422
> 
> 805-438-5600
> 
> www.millersolar.com [6]
> 
> CA Lic. 773985
> 
> From: Jay [mailto:jay.peltz at gmail.com]
> Sent: Saturday, October 28, 2023 1:58 PM
> To: william at millersolar.com; RE-wrenches
> Subject: Re: [RE-wrenches] AC Coupling
> 
> I'm going to both agree and disagree
> 
> Agree The older inverters ( Schneider, Outback, etc) your drawing is 
> correct.
> 
> Disagree For many new inverters ( sol ark, ev4, fortress) they bring ac 
> coupling into the inverter directly.
> 
> Usually on the generator input and not in the backup loads panel.
> 
> And I will also disagree about the statement that these inverters are 
> not designed for ac coupling.
> 
> Agreed that the earlier non rule 21 compliant versions didn't have any 
> internal control and required external relay control to prevent 
> overcharge.
> 
> Newer versions of Schneider, OB, have  frequently shift which works 
> with newer gt inverters to address the ac coupling overcharge concerns. 
> While creating potential new issues for loads with up to 64 hz.
> 
> Jay
> 
> On Oct 28, 2023, at 2:15 PM, William Miller via RE-wrenches 
> <re-wrenches at lists.re-wrenches.org> wrote:
> 
> Friends:
> 
> I am starting to get the impression that there is a diversion on the 
> understanding of the definition of AC coupling within the industry.  I 
> think this definition needs to be clarified.
> 
> Below is a diagram of what I understand is a DC coupled system (I hope 
> these diagrams come through):
> 
> <image003.png>
> 
> A battery inverter that receives AC power into an AC input port is not 
> AC coupled.
> 
> Here is an AC-coupled system:
> 
> <image005.png>
> 
> What makes AC-Coupled systems unique are the problems presented by 
> sending power backwards through a battery inverter.  This is not how 
> battery inverters were originally designed to operate.  These systems 
> require careful consideration to avoid battery overcharging.
> 
> Do we have consensus on this definition?
> 
> William Miller
> 
> Miller Solar
> 
> 17395 Oak Road, Atascadero, CA 93422
> 
> 805-438-5600
> 
> www.millersolar.com [6]
> 
> CA Lic. 773985
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try 
> the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org 
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try 
the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org



Links:
------
[1] http://www.rollsbattery.com
[2] http://www.facebook.com/RollsBattery
[3] https://www.youtube.com/RollsBatteryEngineering
[4] https://www.linkedin.com/company/rolls-battery-engineering
[5] http://www.instagram.com/RollsBattery
[6] http://www.millersolar.com/
[7] 
https://www.youtube.com/watch?v=vRAq9g34VcI&ab_channel=EG4Electronics
[8] https://www.victronenergy.com/live/ac_coupling:start
[9] http://members.sti.net/offgridsolar/
[10] https://offgridsolar1.com/
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20231030/bc25dab2/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: 184db342.png
Type: image/png
Size: 698013 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20231030/bc25dab2/attachment-0001.png>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: grid ac couple.webp
Type: image/webp
Size: 43164 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20231030/bc25dab2/attachment-0001.bin>