This may be far fetched but I have encountered good voltage & low amperage =
no amperage from solar arrays that baffled me on T/S on others systems &
ultimately:
We had voltage & low output amperage to no amperage.
Turns out there was a junction box that had been forgotten about in the
crawl space with never tightened split bolts that were crispy black from
arcing.
There was enough contact for voltage readings & not enough for any amps to
flow.
Double check all connections?