Physically it is all the same. Software is way more complex. As Dave mentioned, you have to follow the commissioning process.
AC1 will no longer accept generator input, it’s grid-only now. So if you have a genset you will need to move that to AC2. This is one of the most irritating changes with the XWPro. Makes dual-generator configs a lot more complex now.
Kevin
From: RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> On Behalf Of Chad Waits via RE-wrenches
Sent: October-24-23 2:18 PM
To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
Cc: Chad Waits <chadwaits at netzerosolar.net>
Subject: [RE-wrenches] XW Drop in replacement inverter
Wrenches,
We have a client that had us construct a solar trailer for them back in 2014-2015 timeframe. The Current XW6048-120/240-60 is cooked and I'm wondering if the Schneider rep (or you savvy off grid guys) on here could tell me if the newer XW Pro 6.8kW 120/240 is an exact drop in replacement for a system including the the old power distribution panel accessories.
Thanks!
Chad Waits