[RE-wrenches] Generator question

Mac Lewis maclewis1 at gmail.com
Tue Sep 26 04:58:17 PDT 2023


Hello Chris,

I think you will find that the generator interaction with the Sol-Ark is
very basic and you won't have much flexibility to do this.

As far as ancillary equipment to do a load start, one idea that comes to
mind is a Victron shunt, Cerbo and GX device.  I'm brainstorming a little
bit here but if you add the shunt into the battery negative cabling, the
Cerbo can be sent the battery current measurement.  The Cerbo could then be
programmed to start based on battery current.  This is a little different
than standard AC load start but it may cover what you need.  Unfortunately,
if the inverter is getting overloaded while its sunny, battery current
alone can't catch the solar current that is being sent directly to the
loads and shutdowns will still occur.

Before you do this, I would suggest contacting Kienan Maxfield of Green-go
Solar Distribution (he's on this list) and knows Victron equipment really
well.  He can probably tell you if I'm off in the weeds...

Let us know what you find out.

On Mon, Sep 25, 2023 at 11:25 AM Dave Angelini Offgrid Solar via
RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:

> I would trigger genset on Soc. Is that what you are doing?
>
>
>
> *Dave Angelini Offgrid Solar
> "we go where powerlines don't"
>    <http://members.sti.net/offgridsolar/>https://offgridsolar1.com/ <https://offgridsolar1.com/>  <http://members.sti.net/offgridsolar/>
> e-mail  offgridsolar at sti.net <offgridsolar at sti.net>
> text 209 813 0060*
>
>
> On 2023-09-25 9:20 am, Chris Daum via RE-wrenches wrote:
>
>      Hi folks:
>
>
>
> We have a situation where the Sol-Ark 12kW Inverter isn’t able to
> adequately manage the loads and perform auto-gen start other than low
> battery level.   And despite thorough understanding of the customer’s
> initial loads, after he’s bought the system, he’s continued to add more and
> more loads – a severe case of load creep.
>
>
>
> He’s got a 38KW generator and we’re looking for the components to make the
> generator *load responsive* instead of just kicking on when the battery
> voltage is low.  Are there any ideas on switching equipment that can do
> this and work with the Sol-Ark?  We’re waiting for a reply from Sol-Ark,
> but thought you folks may have some ideas.
>
>
>
> The original design was for a larger solar system and inverter, but the
> customer balked at the cost and said he’d reduce his loads accordingly.  Unfortunately,
> that has not happened!   Now we’re trying to bend the laws of physics and
> have his 38KW  generator make up the difference. We need to come up with
> a means of accommodating the compromised design and now are faced with
> additional loads -- along with a significantly reduced solar array.   Is
> there a way to make this (2 wire start) generator more load responsive?
>
>
>
> Thanks for any and all advice!
>
>
>
>      Chris Daum
>
>      Oasis Montana Inc.
>
>      406-777-4309 or 4321
>
>      www.oasismontana.com
>
>
>
>
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>

-- 



Mac Lewis

*"Yo solo sé que no sé nada." -Sócrates*
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230926/9ad934ec/attachment.htm>


More information about the RE-wrenches mailing list