[RE-wrenches] sol ark AGS question
Michael Morningstar
mjmorningstar at gmail.com
Fri Sep 15 14:41:00 PDT 2023
Chris,
Just so that I understand correctly, are you saying that new firmware
allows for generator cool down?
On Fri, Sep 15, 2023 at 2:33 PM Jason Szumlanski via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> I saw that setting. I didn't have a chance to look it up today, but I'm
> going back to the site tomorrow. I'm going to play with that and try to get
> rid of the ancillary equipment that is no longer necessary. Thanks for the
> tip.
>
> On Fri, Sep 15, 2023, 5:26 PM Chris Sparadeo <sparadeo.chris at gmail.com>
> wrote:
>
>> In an off-grid scenario I would suggest utilizing the grid connect timer
>> as a Gen warm up. I typically set this qualification time to 30 or 60
>> seconds. Sol Ark fixed the problem with dropping the 2 wire start under
>> full load, so if this is an issue for you, I would update the firmware.
>>
>> On Fri, Sep 15, 2023 at 4:56 PM Jason Szumlanski via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> I just replaced two Sunny Islands and one Sunny Boy that I did not
>>> install with a single Sol-Ark 15k today. The generator installer (not me)
>>> had already installed a custom but simple time delay relay. I didn't get
>>> into the logic of it, but from what I understand the generator already had
>>> a cool-down period when remote start signal is lost, but no warm up delay.
>>>
>>> Major deficiency? I think that is actually pretty accurate and Sol-Ark
>>> should fix it, but it isn't too hard to take care of it another way.
>>>
>>> I wonder if this has something with the distinction of accepting
>>> generator input on the grid input as well. You would not want a grid delay
>>> if it were a utility. Still, they should be able to build in that logic I
>>> would think.
>>>
>>> Jason Szumlanski
>>> Principal Solar Designer | Florida Solar Design Group
>>> NABCEP Certified Solar Professional (PVIP)
>>> Florida State Certified Solar Contractor CVC56956
>>>
>>>
>>> On Fri, Sep 15, 2023 at 8:28 AM Michael Morningstar via RE-wrenches <
>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>
>>>> We learned of this major deficiency after an eight unit install. No
>>>> cool down is disastrous to modern diesels. Our work around was installing a
>>>> 400amp contactor and macromatic programmable relay.
>>>>
>>>> On Thu, Sep 14, 2023 at 10:05 PM Jerry Shafer via RE-wrenches <
>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>
>>>>> Jay, wrenches
>>>>> ASCO makes multiple ATS controls that can manage delays latching up
>>>>> and for cool down. Most of the gensets have are programmed cool down after
>>>>> relay opens so its not an issue. Generally on start up the genny connects
>>>>> as soon as it's voltage and freq are within range.
>>>>> fun times
>>>>>
>>>>>
>>>>>
>>>>> On Thu, Sep 14, 2023, 2:26 PM jay via RE-wrenches <
>>>>> re-wrenches at lists.re-wrenches.org> wrote:
>>>>>
>>>>>> Hi All,
>>>>>>
>>>>>> I have a client with a sol ark and it doesn’t have warm up or cool
>>>>>> down, kind of amazing companies are going backwards in their tech.
>>>>>>
>>>>>>
>>>>>> Has anyone come up with external fix for this?
>>>>>>
>>>>>> I am guessing the internal relay on the sol ark switches closed when
>>>>>> it sees the correct volts/hz and opens the sol ark relay when it sends the
>>>>>> off signal.
>>>>>>
>>>>>> If thats correct I can pretty easily use a delay relay on the off
>>>>>> cycle assuming the on signal has a time window to allow for this delay in
>>>>>> sending power to the inverter.
>>>>>>
>>>>>> The on delay I don’t see anyway unless I use a contactor with on
>>>>>> delay relay.
>>>>>>
>>>>>> Maybe there is a off the shelf generator transfer switch that has
>>>>>> this built in?
>>>>>>
>>>>>> Thanks in advance
>>>>>>
>>>>>> Jay
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>>
>>>>>> _______________________________________________
>>>>>> List sponsored by Redwood Alliance
>>>>>>
>>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>>
>>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>>
>>>>>> Change listserver email address & settings:
>>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> There are two list archives for searching. When one doesn't work, try
>>>>>> the other:
>>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>>
>>>>>> List rules & etiquette:
>>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>>
>>>>>> Check out or update participant bios:
>>>>>> http://www.members.re-wrenches.org
>>>>>>
>>>>>> _______________________________________________
>>>>> List sponsored by Redwood Alliance
>>>>>
>>>>> Pay optional member dues here: http://re-wrenches.org
>>>>>
>>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>> Change listserver email address & settings:
>>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>>
>>>>> There are two list archives for searching. When one doesn't work, try
>>>>> the other:
>>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>>
>>>>> List rules & etiquette:
>>>>> http://www.re-wrenches.org/etiquette.htm
>>>>>
>>>>> Check out or update participant bios:
>>>>> http://www.members.re-wrenches.org
>>>>>
>>>>>
>>>>
>>>> --
>>>>
>>>> Michael Morningstar
>>>>
>>>>
>>>> Morningstar Electric
>>>>
>>>> PO Box 1494
>>>>
>>>> Mount Shasta, CA 96067
>>>>
>>>> 530-921-0560
>>>>
>>>> mjmorningstar at gmail.com
>>>>
>>>>
>>>> _______________________________________________
>>>> List sponsored by Redwood Alliance
>>>>
>>>> Pay optional member dues here: http://re-wrenches.org
>>>>
>>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>>
>>>> Change listserver email address & settings:
>>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>>
>>>> There are two list archives for searching. When one doesn't work, try
>>>> the other:
>>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>>
>>>> List rules & etiquette:
>>>> http://www.re-wrenches.org/etiquette.htm
>>>>
>>>> Check out or update participant bios:
>>>> http://www.members.re-wrenches.org
>>>>
>>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
--
Michael Morningstar
Morningstar Electric
PO Box 1494
Mount Shasta, CA 96067
530-921-0560
mjmorningstar at gmail.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230915/44ce65b9/attachment.htm>
More information about the RE-wrenches
mailing list