[RE-wrenches] High current dc combiner vibration

Starlight larry at starlightsolar.com
Thu Jun 29 09:24:48 PDT 2023


You may already know but… Are your DC cables bonded together and twisted where possible to reduce magnetic fields? Higher the current and greater the loop area, the stronger the fields are. More parallel loops, the greater the combined flux = loud Hums.  

Larry Crutcher
Starlight Solar Power Systems




On Jun 29, 2023, at 8:19 AM, Kirk Herander via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:

All, 

I am in the middle of commissioning a 480kwh BP LFP battery bank, connected to -10- OB Radian 8kw inverter/chargers.

For the DC combiner I am using midnite 2000 amp combiner boxes, modified to mount  class T fuses on the positive bus, for both battery inputs and inverter outputs.

For starters, I set the master inverter at a max charge rate of 20 AC amps, which equates to a DC charge of about 74 A. All the other inverters are automatically set to this charge rate as well.

Turning the chargers on one by one, I started to get quite an audible vibration from the combiner box at a combined charge of about 400 to 500 A. 

So I took the cover off of the combiner, which was vibrating noticabllly by feel. Most of the noise was from the cover not fitting tight. But the The box itself is also vibrating by feel.

I took the combined charge up to 640A dc. This level of vibration definitely increases with an increased charge rate. And I am surprised because after all, we’re not talking AC here we’re talking DC. It almost reminds me of a large AC transformer in its behavior. The vibration did not seem to be originating at the inverters, then resonating to the combiner.

I can dampen the vibration by adding a few things, but I’m surprised that this is happening. All connections in the combiner are tightened properly. Ideas?










-- 
Kirk Herander /  <>kirkh at vermont.solar <mailto:kirkh at vermont.solar>
Owner|Principal, VT Solar, LLC
Celebrating our 32st Anniversary 1991-2023!!
dba Vermont Solar Engineering
802.863.1202
_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230629/9d087ac6/attachment.htm>


More information about the RE-wrenches mailing list