[RE-wrenches] Remote battery disconnects
Christopher Warfel
cwarfel at entech-engineering.com
Sat Jan 28 06:28:10 PST 2023
Seems confusing that the AHJ is requiring a disconnect for AC wiring,
not specific to which or both panel types, and then a dc disconnect with
no code reference. Was trying to convey a reasonable, safe approach. A
lot of bad information from fire department solar consultants making a
lot of money fear mongering, which has led to this type of situation. Chris
On 1/27/2023 3:35 PM, William Miller via RE-wrenches wrote:
>
> Glenn:
>
> As I wrote, a DC disconnect is required. Here is an excerpt from the
> Q&A with the building official:
>
> 4.Will you be requiring an external disconnect to disconnect the AC
> output of the inverter system from premise wiring?
>
> Yes, as required per 230.85
>
> 5.Will you be requiring an external disconnect to disconnect batteries
> from the inverters?
>
> Yes
>
> If the DC disconnect was not required I would not be wasting
> everyone’s time with my post. I try to be careful about that,
> researching on my own before posting and trying to make my questions
> very clear. I also try not to embarrass myself with dumb questions,
> but that does happen occasionally…
>
> William
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600
>
> www.millersolar.com <http://www.millersolar.com/>
>
> CA Lic. 773985
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org]
> *On Behalf Of *Glenn Burt via RE-wrenches
> *Sent:* Friday, January 27, 2023 11:46 AM
> *To:* William Miller via RE-wrenches
> *Cc:* Glenn Burt
> *Subject:* Re: [RE-wrenches] Remote battery disconnects
>
> Does the AHJ really want the batteries disconnected from conductors,
> or does he really just want the inverters to stop operating and
> producing AC within the house?
>
> Obviously there is a big difference here and it may be changing as the
> code evolves.
>
> -Glenn
>
> Sent from my 'smart'phone, so please excuse typos and spelling errors.
>
> ------ Original message------
>
> *From: *William Miller via RE-wrenches
>
> *Date: *Fri, Jan 27, 2023 2:26 PM
>
> *To: *RE-wrenches;
>
> *Cc: *William Miller;
>
> *Subject:*[RE-wrenches] Remote battery disconnects
>
> Friends:
>
> We have a large-ish residential off-grid system install coming up.
> The AHJ has said they will require a remote battery disconnect. I
> suspect there will be fire sprinkler controls and a pressure pump that
> would become inoperable if this system were engaged. In this case we
> will apply for a waiver.
>
> The last time this was discussed here as far as I can find was October
> of 2020. At that time no one suggested any specific battery
> disconnect equipment.
>
> To further clarify my needs: There will be 4 or 5 Radian 8048
> inverters (5 or 6 4/0 battery circuits, ~350A each) and two 175 amp PV
> recombiner outputs. That is 6 poles of high amperage DC disconnects.
>
> The battery array will be either a UnigyII VRLA or a lithium of a
> brand yet to be determined. In the case of lithium we will look for a
> system that can remotely enable a BMS shutdown. In the case of a VRLA
> lead-acid, we will not have that luxury.
>
> I have done some considerable research and have not found viable, high
> amperage, remotely activated shutdown equipment.
>
> I am wondering what hardware others may be using to achieve remote
> battery disconnecting in these types of cases..
>
> William
>
> Miller Solar
>
> 17395 Oak Road, Atascadero, CA 93422
>
> 805-438-5600 <tel:805-438-5600>
>
> www.millersolar.com <http://www.millersolar.com/>
>
> CA Lic. 773985
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here:http://re-wrenches.org
>
> List Address:RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230128/d541d7dd/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230128/d541d7dd/attachment-0001.jpg>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: cwarfel.vcf
Type: text/vcard
Size: 203 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230128/d541d7dd/attachment-0001.vcf>
More information about the RE-wrenches
mailing list