[RE-wrenches] Low Frequency transformer off-grid inverter options

Jay jay.peltz at gmail.com
Fri Jan 13 11:57:33 PST 2023


Hi Mac

The radian is low voltage transformer
Based. Has hella surge capacity 

I would consider what web based monitoring system he wants and go with that platform. 

Regardless of system I’d install soft start/vfd on the larger units. Just easier on everything.

The solark 12 doesn’t seem to be good for larger loads and doesn’t do out of balance well, and limited to 6kw per phase. The new 15 might be better, not sure. Numerous YouTube videos showing side by side vs XW and radian. Both run stuff over their rating which the SolA won’t run even though its under its rating. 

Good luck

Jay








> On Jan 13, 2023, at 11:34 AM, Mac Lewis via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
> 
> 
> Hello Wrenches,
> 
> I have a new client that has ran a pretty decent wood shop for about 10 years on a Magnum 4448.  He's got some large loads, planers, saws, compressors vacuums etc.  They are really nice, heavy duty pieces of equipment.  Amazingly, the Magnum has been able to start these loads for the most part for 10 years, but he has reported that it has gotten worse lately (could be a load issue), brown outs, dimming etc
> 
> He wants to upgrade the system, get remote monitoring etc.  I tried a test with a Sol-Ark 12, and it won't start these large motor loads.  I was a little surprised by that but I know they aren't as good as the low freq transformer based inverters at these surges.
> 
> I confirmed that its not just an overload from imbalance because the 240V loads will also overload it.  I got an inrush measurement of 48.5A Ac @240 (but it didn't start the load before Sol-Ark would shut off)  
> 
> What are my options?
> Schneider XW Pro 6848
> Outback Radian 8048 (Is this a low freq device?)
> Sunny Islands are beasts but weird to work with and not user friendly
> 
> Any others I should consider?  He does have some significant 120 only loads so I don't think the Outback vfxr are a good choice.
> 
> Is it as simple as saying if the Magnum can start this load, the Radian should?
> 
> I appreciate your input!
> 
> --
> Mac Lewis
> 
> "Yo solo sé que no sé nada." -Sócrates
> 
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> Pay optional member dues here: http://re-wrenches.org
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
> 
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> http://www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20230113/74fb0670/attachment.htm>


More information about the RE-wrenches mailing list