[RE-wrenches] Outback vfx 3648 question
Jay
jay.peltz at gmail.com
Wed Jan 4 06:06:17 PST 2023
Hi john
Good to hear from you.
Your system charges at above Outback programmed amp setpoints?
And in a sort of cyclical way? Sometimes it’s normal for an hour then will go to 2x charge rate then back down then maybe 1.5.
I talked to a senior Outback tech and they haven’t heard of this issue.
But if you say is true, how do you adjust the settings so it won’t trip the generator breaker?
This one is already at 5aac on ac input and 5 aac on charge and it will still, not often trip the generator breaker.
Thx
Jay
> On Jan 3, 2023, at 8:13 PM, John Blittersdorf via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
> Jay,
> I have seen this a few times but usually with a generator that is not
> designed for hard wired system. I have a Ryobi
> work generator that does this on both of my outback systems. It says
> in the instructions that it is not to be used for stationary
> applications (ie normally grounded systems).
>
> John
>
>> On Tue, Jan 3, 2023 at 9:16 AM Jay via RE-wrenches
>> <re-wrenches at lists.re-wrenches.org> wrote:
>>
>> Has anyone had a vfx sort of not pay attention to it charging current settings,
>>
>> I have a customer who’s older vfx will do the following
>>
>> Settings are 5 amps ac, 5 amp ac charge
>>
>> It’ll run at about 10 amps dc charging
>> Then randomly go up to 30 amps dc then back down. Maybe 15 seconds
>> Later go up to 25 amps and back down. Kinda all over the place
>>
>> Then will stay at the lower amps for some period of time.
>>
>> I’m thinking it’s a hardware problem?
>>
>> And given the age a new board set is probably in order.
>>
>> Thoughts?
>>
>> Thx
>> Jay
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
More information about the RE-wrenches
mailing list