[RE-wrenches] Old Trace SW inverter connected to the grid.

Foxfire Energy dan at foxfire-energy.com
Mon Dec 19 09:20:35 PST 2022


I’m thinking the simple fix is to just make sure the breaker between the grid and inverter is off when you’re running the generator.. JMHO..

Sent from my iPhone

On Dec 19, 2022, at 10:52 AM, Tump via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:

 I have neve heard that but I would connect the utility to the AC1 input as the window is quite narrow then the grid. The GTI was a piss poor way for trace to regulate “sell” current would ramp up & back down all day long. NOT necessary. BUT then again that old duffer; SH  probably has more brain cells left then I do.
On Dec 19, 2022, at 10:27 AM, Chad Waits via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:

I thought the SW needed a Grid Tie Interface (GTI)<https://www.altestore.com/store/media/pdfs/xantrex/Grid%20Tie%20Interface%20(GTI)%20Data%20Sheet.pdf> to keep current from leaking out to the grid even if you didn;t want to sell to them...

Chad Waits
President - Net Zero Solar
945 W. Silverlake, Tucson, AZ 85713
Cell: (520) 270-4873
[https://ci3.googleusercontent.com/mail-sig/AIorK4zMcUl5EhjemfzUnd46zPDuJwyFURzd7bNuklolvQ37rwiNtc0YPbqwUUg3S1lnCs0T7PyfxVg]


On Mon, Dec 19, 2022 at 8:21 AM David Palumbo via RE-wrenches <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>> wrote:
Wrenches,

I have been retired from doing solar installs for 10 years now and I am reaching out for help as to recommending a solution to an old do-it-yourself customers question.
His solar system that was formerly off-grid and is now using grid power instead of a back up generator.
He had/has no intention of doing a net-metered system. Just trying to reduce dependance on a fossil fuel genset during our mostly sunless Vermont winters.

He says that he brought in power a few years ago to run their expanding maple sugaring operation located next to their house. At that time they ran a 115Vac circuit (grid power) over to their house and connected grid power into AC Hot In terminal #! in their Trace SW 2512. This is correct as I see terminal #2 is labeled for generator power.
He has the Trace programmed for float mode  not sell mode.

Their local utility was working on the line nearby on the main road and noticed a small amount of current flowing into the grid and figured out where it was coming from. The utility did not immediately shut him down. Just told him to correct the problem. He is asking me for advice.

My first inclination is to separate the grid power completely from the inverter power and to feed both power sources into a double pole double throw transfer switch. What other options should be considered.

Thanks in advance and happy holidays,

Dave Palumbo
Formerly > Independent Power & Light
Hyde Park, VT
802-371-8678 voice or text


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org<http://re-wrenches.org/>

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org<http://www.members.re-wrenches.org/>

_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org


Tump<blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net>3391 at gmail.com<mailto:3391 at gmail.com>       www.SWNL.net<blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
                Solarwinds Northernlights
       Serving Mid Coast Maine & Northern California
                         207-832-7574   Cl. 610-517-8401
                              Blair "TUMP" May

               ********  MAINE'S CHARTER ********
                      NABCEP    "Certified PV Installer"

              ********  MAINE'S CHARTER ********
                  Trace Xantrex "Certified" Dealer / Installer"




_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: http://re-wrenches.org

List Address: RE-wrenches at lists.re-wrenches.org

Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org

There are two list archives for searching. When one doesn't work, try the other:
https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org

List rules & etiquette:
http://www.re-wrenches.org/etiquette.htm

Check out or update participant bios:
http://www.members.re-wrenches.org

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20221219/618732bd/attachment.htm>


More information about the RE-wrenches mailing list