Hi Lloyd, Did you tie into the 12VDC of the SolArk with the lock
pushbutton switch?
On 11/18/2022 10:47 AM, Lloyd Hoffstatter wrote:
> Chris,
> For emergency shutoff switch i just used a lock pushbotton switch in a
> clear front lockable box with an led to indicate status. We did use an
> external power supply because we were using Tigo optimizers, CCA and TAP.
> Best regards,
> Lloyd
>
> Get Outlook for iOS <https://aka.ms/o0ukef>
> ------------------------------------------------------------------------
> *From:* RE-wrenches <re-wrenches-bounces at lists.re-wrenches.org> on
> behalf of Christopher Warfel via RE-wrenches
> <re-wrenches at lists.re-wrenches.org>
> *Sent:* Friday, November 18, 2022 10:14:52 AM
> *To:* Bradley Bassett <bbassett2 at gmail.com>; RE-wrenches
> <re-wrenches at lists.re-wrenches.org>
> *Cc:* Christopher Warfel <cwarfel at entech-engineering.com>
> *Subject:* Re: [RE-wrenches] SolArk and Tigo compatibility
>
> Thanks everyone, the person I started with a SolArk asked me to call
> them, so I've left a message. I'll let everyone know what the
> determination is. Bradley raises a good point about shutting down the
> back up loads panel. We would like to have an outdoor accessible
> disconnect switch between the back up loads panel and the inverter so
> that can happen more easily for first responders. I have to go back
> and understand a few more things and will let you know. Thanks again.
> Chris
>
> On 11/16/2022 10:14 PM, Bradley Bassett wrote:
>> The issue as I see it is that the Tigo RSS Transmitter and the
>> APsmart transmitter are both rated to draw up to 800ma. The 12VDC
>> output of the Sol-Ark inverters is limited to 100ma. Since some have
>> used this successfully I suppose that means that either these
>> transmitters don't really use more than 100ma, or the 12VDC output of
>> the Sol-Ark can actually handle more than that, or some combination
>> of both. If I owned a Sol-Ark I'd test this to see what the answer
>> is, but alas I do not. I design systems using a 48VDC to 12VDC power
>> supply (Online Components has a Mean-Well device for a reasonable
>> price, sorry no link from here) and a fairly rare IMO shutdown button
>> (we have that) that has both NO and NC contacts. This is needed
>> because to shut down the Sol-Ark inverter requires a NO contact that
>> closes on initiation which is quite rare in RSD initiators. And you
>> do still need to shut down the inverter as well as the RSD devices so
>> that it does not continue to feed voltage back into the PV circuits
>> (I think). This also shuts down the AC output of the Sol-Ark which
>> tends to make the inspector happy. Since it also shuts down the
>> inverter, that limits the battery to its own circuits, does this
>> count as a battery disconnect also?? I'm seeing some inspectors
>> calling out for battery disconnects which is much more problematic.
>>
>> Brad Bassett
>> AEE Solar
>>
>> On Wed, Nov 16, 2022 at 4:27 PM Jerry Shafer via RE-wrenches
>> <re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>
>> Wrenches, Christopher
>> I have done quite a few and per solark have always connected in
>> the inverter with no issues, Now with that connecting to the
>> output side it would do much the same work until it did not then
>> shut off the modules.
>> Fun times
>>
>> On Wed, Nov 16, 2022 at 6:33 AM Christopher Warfel via
>> RE-wrenches <re-wrenches at lists.re-wrenches.org
>> <mailto:re-wrenches at lists.re-wrenches.org>> wrote:
>>
>> Hi, We are doing our first system with these two devices. The
>> inverter is SolArk 12P (mutimode) and the Tigo product for RS
>> is the TS4F. Tigo has me a little bit walking in circles.
>>
>> I told them that SolArk says not to use the 12VDC RS output
>> terminals for connecting the transmitter. I gave them the
>> attached drawing which they ask for, which shows the
>> transmitter connected to a 120VAC/12VDC breaker which they
>> supply. They told me to wire the 120VAC source to the main
>> service panel so the array would shut down on loss of power.
>> I told them that is exactly NOTwhat I wanted to happen as
>> that would stop the battery charging when there is a loss of
>> utility power. I said I wanted the 120VAC source to be the
>> back up loads panel. After about a week of calls and emails,
>> I got an email back saying to use the SolArk 12VDC terminals
>> for RS. I just emailed them a screen shot of the SolArk
>> manual that says not to do that.
>>
>> At this point, I am asking anyone on the list to let me know
>> how they wired the transmitter successfully. Thank you for
>> any guidance, Chris Warfel
>>
>>
>>
>>
>>
>> --
>> Christopher Warfel
>> ENTECH Engineering, Inc.
>> PO Box 871, Block Island, RI 02807
>> 401-466-8978
>> <http://entech-engineering.com>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>> <http://re-wrenches.org>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>> There are two list archives for searching. When one doesn't
>> work, try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> <http://www.members.re-wrenches.org>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>> <http://re-wrenches.org>
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>> <mailto:RE-wrenches at lists.re-wrenches.org>
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>>
>> There are two list archives for searching. When one doesn't work,
>> try the other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> <https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/>
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>> <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org>
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>> <http://www.re-wrenches.org/etiquette.htm>
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>> <http://www.members.re-wrenches.org>
>>
> --
> Christopher Warfel
> ENTECH Engineering, Inc.
> PO Box 871, Block Island, RI 02807
> 401-466-8978
> <http://entech-engineering.com>
>
>
--
Christopher Warfel
ENTECH Engineering, Inc.
PO Box 871, Block Island, RI 02807
401-466-8978
<http://entech-engineering.com>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20221118/f92ead79/attachment-0001.htm>
-------------- next part --------------
A non-text attachment was scrubbed...
Name: EEIlogolong.jpg
Type: image/jpeg
Size: 17117 bytes
Desc: not available
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20221118/f92ead79/attachment-0001.jpg>
More information about the RE-wrenches
mailing list