[RE-wrenches] Magnum inverter/generator integration problems
Jay
jay.peltz at gmail.com
Mon Jul 25 16:16:18 PDT 2022
Hi Chris.
I’m a bit confused about the breaker on the BMK. That’s the battery monitor? No breakers.
If you mean the inverter, then check that both legs are working. I’ve had a similar issue in the past that turned out to be a bad 240v breaker. 1 side didn’t work, but because of how the magnum works if you check volts it will read right.
Have to check with clamp on for current
The inverter overloads with 120v input, and yeah takes about 10-15 minutes. Might give it a check.
Jay
> On Jul 25, 2022, at 12:08 PM, Chris Daum via RE-wrenches <re-wrenches at lists.re-wrenches.org> wrote:
>
>
> Hi folks, I’m trying to help a fellow with two Magnum Systems; one of them will accept his Honda EG5000CL gen set, the other will not.
> After running for a bout 10~15 minutes the circuit breaker pops on the BMK. He will be rebooting his BMK this evening in the first attempt at getting his system back up. He has been powering this system with a Predator 3500w Gen set, along with his solar array.
> The system will not accept the Honda. Any ideas of clues to check out?
>
> Sincerely,
>
> Chris Daum
> Oasis Montana Inc.
> 406-777-4321
> www.oasismontana.com
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20220725/50a57757/attachment.htm>
More information about the RE-wrenches
mailing list