[RE-wrenches] Outback FXR: Battery voltage exceeds settings
Nicholas Welch
welch.nicholas.r at gmail.com
Sat Jul 23 09:20:19 PDT 2022
Is there an FNDC on this system? I’ve experienced some of the same issues
when the FNDC terminations were loose.
On Sat, Jul 23, 2022 at 11:56 AM Jay via RE-wrenches <
re-wrenches at lists.re-wrenches.org> wrote:
> Outback controllers have a tendency to be a bit slow.
>
> So they can definitely get higher than the set points but only for a
> second or two which is not going do damage anything. I’ve seen them do
> this.
>
> Especially if it’s a larger array, sealed batteries and when the batteries
> are full and a load turns on and then off.
>
> At the load off the CC is dumping watts, and the sudden loss means a short
> voltage spike.
>
> Jay
>
>
>
>
> On Jul 23, 2022, at 9:43 AM, Jerry Shafer via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>
>
> Most AGM's don't like voltage that high and it swells the battery and
> destroys its storage capability alot of the time
> Jerry
>
> On Fri, Jul 22, 2022, 7:50 PM Steve Higgins via RE-wrenches <
> re-wrenches at lists.re-wrenches.org> wrote:
>
>> William,
>>
>> If the battery cases swelled, they saw over 52 degrees C temps for quite
>> some time.
>>
>> While the swelling is usually only cosmetic, what's happening inside is
>> the negative plates are starting to burn. This is where you will start to
>> lose capacity and life cycle... Extended temps of just 35C will half the
>> overall battery life.
>>
>> One of the issues with the Outback gear is they only temp compensate at
>> 5mv/Degree/cell. For all the AGM batteries I know of, you need to temp
>> compensate at 4mv. In hot temps, this should help, but cold temps could
>> result in an overcharge. Did you check the BTS and make sure it was
>> operating properly?
>>
>> Another issue is that BTSs are often placed on the top or lug of the
>> battery, The top of the battery is about 5-10 deg C cooler than 1/2 way
>> down the side of the battery, Which will also cause problems with proper
>> temperature compensation, especially with warmer/colder extremes.
>>
>> Any kind of sulfation will cause an imbalance when you mix old and new
>> batteries. I'm not a fan of mixing any age AGM batteries as there is no
>> way to tell what the SOC of the old bank vs. the new bank is. They are
>> not like flooded batteries; you can check SGs and dissipate heat
>> much better than AGM or GEL batteries. I discourage doing this if you
>> can. I probably wouldn't have mixed the old and new in the same strings.
>> This way, you keep the higher resistance batteries in a single string,
>>
>> Lastly, bunching them together with no spacing between them is very bad.
>> Batteries should be in a cool, dry environment. Most battery companies
>> want to see 1-3 inches in between each battery to allow for effective
>> cooling. When they are all bunched up together, that is a lot of thermal
>> mass that doesn't have much chance of cooling. I have seen two parallel
>> strings of AGMs take 24-36 hours with no charging or load to drop from 45c
>> to 25C!
>>
>> Hope this helps! Have a good weekend.
>>
>>
>>
>>
>> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
>> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
>> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
>> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
>> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
>> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
>> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
>> <http://www.rollsbattery.com> <http://www.rollsbattery.com>
>> <http://www.rollsbattery.com>
>> Steve Higgins ⋅ Technical Services Manager
>> t +1.902.597.4020 m +1.206.790.5840
>> f +1.902.597.8447 e steve at surrette.com
>>
>> <#m_-4178165466314050815_m_-3124562702126219588_SignatureSanitizer_SafeHtmlFilter_>
>> <http://www.facebook.com/RollsBattery>
>> <http://www.facebook.com/RollsBattery>
>> <http://www.twitter.com/RollsBattery>
>> <https://www.youtube.com/user/RollsBattery>
>> <https://www.linkedin.com/company/rolls-battery-engineering>
>> <http://www.instagram.com/RollsBattery>
>> <http://www.instagram.com/RollsBattery>
>> <http://www.instagram.com/RollsBattery>
>>
>>
>> ------------------------------
>> CONFIDENTIALITY: The information transmitted herein is intended only for
>> the addressee and may contain confidential, proprietary and/or privileged
>> material. Any unauthorized review, distribution or other use of or the
>> taking of any action in reliance upon this information is prohibited. If
>> you receive this email in error, please contact the sender and delete or
>> destroy this message and all copies.
>> ------------------------------
>>
>>
>> On Fri, Jul 22, 2022 at 6:48 PM William Miller via RE-wrenches <
>> re-wrenches at lists.re-wrenches.org> wrote:
>>
>>> Friends:
>>>
>>>
>>>
>>> I maintain a system with 16 AGM L-16 batteries. Eight were installed in
>>> September of 2021 and 8 were added in March of 2022. This is 5 months
>>> apart. I have understood that when you install a string of batteries you
>>> have one year in which to add another string before the first string ages
>>> to the point it is contraindicated. When I added the second 8 I put 4 new
>>> batteries and 4 old batteries in each string.
>>>
>>>
>>>
>>> About a third of the batteries are discovered to bulging on top. I
>>> assume this means the batteries are damaged. I checked the FXR and Outback
>>> Extreme Charge controller settings and all were set to absorb at 58.8, and
>>> float at 55.2, as the manufacturer recommends.
>>>
>>>
>>>
>>> I downloaded the charge controller log and got 129 days of data. In
>>> that log I see 68 days where the batteries exceeded 60 VDC. This is over
>>> half the days.
>>>
>>>
>>>
>>> I wonder this:
>>>
>>>
>>>
>>> 1. Why did the voltage go up above 58.8 on so many days even though
>>> it was set at 58.8. (I set the EQ voltage at 58.8 just in case, but EQ was
>>> never engaged.)
>>>
>>> 2. Did the excess voltage damage the batteries?
>>>
>>> Any input is appreciated.
>>>
>>>
>>>
>>> Sincerely,
>>>
>>>
>>>
>>> William Miller
>>>
>>>
>>>
>>> Miller Solar
>>>
>>> 17395 Oak Road, Atascadero, CA 93422
>>>
>>> 805-438-5600
>>>
>>> www.millersolar.com
>>>
>>> CA Lic. 773985
>>>
>>>
>>>
>>>
>>> _______________________________________________
>>> List sponsored by Redwood Alliance
>>>
>>> Pay optional member dues here: http://re-wrenches.org
>>>
>>> List Address: RE-wrenches at lists.re-wrenches.org
>>>
>>> Change listserver email address & settings:
>>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>> There are two list archives for searching. When one doesn't work, try
>>> the other:
>>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>>
>>> List rules & etiquette:
>>> http://www.re-wrenches.org/etiquette.htm
>>>
>>> Check out or update participant bios:
>>> http://www.members.re-wrenches.org
>>>
>>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> Pay optional member dues here: http://re-wrenches.org
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> There are two list archives for searching. When one doesn't work, try the
>> other:
>> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
>> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>>
>> List rules & etiquette:
>> http://www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> http://www.members.re-wrenches.org
>>
>> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> Pay optional member dues here: http://re-wrenches.org
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> There are two list archives for searching. When one doesn't work, try the
> other:
> https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/
> http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org
>
> List rules & etiquette:
> http://www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> http://www.members.re-wrenches.org
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20220723/30a1411a/attachment.htm>
More information about the RE-wrenches
mailing list