[RE-wrenches] AC Coupled Enphase

Drake drake.chamberlin at redwoodalliance.org
Wed Aug 30 05:54:16 PDT 2017


Hi boB,

Would there be any issues with delayed control of 
the microinverters? We do  plan to  use disconnects for maintenance.

Thanks,

Drake

At 06:27 PM 8/29/2017, you wrote:
>Content-Type: multipart/alternative;
>  boundary="------------155C815B9802686293824DDD"
>Content-Language: en-US
>
>
>SSRs, especially AC SSRs made from thyrisotrs 
>(scrs and/or triacs)Â  are "leaky" in general
>
>so when turned OFF, can cause a 
>shock....  Maybe not enough to kill you but maybe enough
>
>to make you fall off the roof !
>
>I'm not sure why the disconnects aren't good 
>enough which should already be in place ?
>
>boB
>
>On 8/29/2017 4:53 AM, Jason Szumlanski wrote:
>>My vote would still be to use two single pole 
>>relays as suggested previously to kill each 
>>leg. That way you build in redundancy and 
>>dropping either leg will do the trick. In fact, 
>>it sounds like this would be even better than a 
>>two pole relay for the redundancy reason.
>>
>>The other factor is whether you are using NO or 
>>NC relays. My engineer requires NO relays in 
>>these cases so they would fail in the open 
>>position only. I'm not sure how this would 
>>work, or if it would work with solid state 
>>relays. I have never dug into this. My 
>>understanding is that solid state relays fail 
>>in the closed condition (shorted). This would 
>>preclude their use in a situation where opening 
>>the circuit is the preferred failure mode. 
>>Maybe someone with some more knowledge in this 
>>area can chime in on whether SSRs are a good idea in this scenario.
>>
>>Jason Szumlanski
>>
>>
>>On Mon, Aug 28, 2017 at 10:19 PM, Nick Soleil 
>><<mailto:nsoleil at enphaseenergy.com>nsoleil at enphaseenergy.com> wrote:
>>The one-pole relay will work for de-energizing 
>>any of the Enphase microinverters.
>>
>>Nick Soleil
>>Field Application Engineer
>>Enphase Energy
>>Cell: <tel:%28707%29%20321-2937>707-321-2937
>>
>>On Aug 28, 2017, at 6:03 PM, Drake 
>><<mailto:drake.chamberlin at redwoodalliance.org>drake.chamberlin at redwoodalliance.org> 
>>wrote:
>>
>>>Hi Nick,
>>>
>>>I should mention that the inverters being AC 
>>>coupled are M-250s, not the new IQ series. Would that make any difference?
>>>
>>>Thanks,
>>>
>>>
>>>Drake
>>>
>>>
>>>At 03:12 PM 8/28/2017, Drake wrote:
>>>>Hi Nick,
>>>>
>>>>
>>>>At 11:20 AM 8/28/2017, you wrote:
>>>>>Content-Language: en-US
>>>>>Content-Type: multipart/alternative;
>>>>>Â Â Â Â Â Â Â 
>>>>>Â  boundary="_000_56449940CA694DDAABB811FCC45A2070enphaseenergycom_"
>>>>>
>>>>>You can use a one-pole relay.  We show 
>>>>>one-pole switching in our zero-export, 
>>>>>self-consumption doc for PEL applications.
>>>>>
>>>>>Nick Soleil
>>>>>Field Application Engineer
>>>>>Enphase Energy
>>>>>Cell: <tel:%28707%29%20321-2937>707-321-2937
>>>>>
>>>>>On Aug 28, 2017, at 6:44 AM, Drake 
>>>>><<mailto:drake.chamberlin at redwoodalliance.org 
>>>>> > drake.chamberlin at redwoodalliance.org> wrote:
>>>>>
>>>>>>Hello Wrenches,
>>>>>>
>>>>>>I am going to AC couple some Enphase 
>>>>>>inverters and found some really nice solid 
>>>>>>state, single pole relays to control them 
>>>>>>with. Enphase says I must use 2 pole relays 
>>>>>>for the control current even though the 
>>>>>>disconnects will turn off all power for maintenance.
>>>>>>
>>>>>>Enphase claims that the inverters will not 
>>>>>>shut down reliably with only one line 
>>>>>>opened. This does not make sense to me in 
>>>>>>view of UL 1741. Is Enphase correct in 
>>>>>>their claim, or are there other reasons that both poles need to be opened
>>>>>>
>>>>>>I want to use the solid state relays 
>>>>>>because the coil voltage is between 3 and 
>>>>>>32 volts. This would avoid the need to add 
>>>>>>voltage dropping series resistors to 
>>>>>>protect the coil for higher battery voltages.
>>>>>>
>>>>>>Alternatively, does anyone know of 
>>>>>>reasonably priced, 2 pole solid state relays?
>>>>>>
>>>>>>Thanks,
>>>>>>
>>>>>>Drake
>>>>>>
>>>>>>Â
>>>>>>Drake Chamberlin
>>>>>>Athens Electric LLC
>>>>>>OH License 44810
>>>>>>CO License 3773
>>>>>>NABCEP Certified Solar PV
>>>>>><tel:%28740%29%20448-7328>740-448-7328
>>>>>>
>>>>>>_______________________________________________
>>>>>>List sponsored by Redwood Alliance
>>>>>>
>>>>>>List Address: 
>>>>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>>>>
>>>>>>Change listserver email address & settings:
>>>>>><https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>>>
>>>>>>
>>>>>>List-Archive: 
>>>>>><https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>>>>>>
>>>>>>
>>>>>>List rules & etiquette:
>>>>>><https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>www.re-wrenches.org/etiquette.htm
>>>>>>
>>>>>>Check out or update participant bios:
>>>>>><https://mailtrack.io/trace/link/42b8962882456a240060cea7f870a550cf549bc6?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=8682c7a34db623bd>www.members.re-wrenches.org
>>>>>_______________________________________________
>>>>>List sponsored by Redwood Alliance
>>>>>
>>>>>List Address: 
>>>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>>>
>>>>>Change listserver email address & settings:
>>>>><https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>>
>>>>>
>>>>>List-Archive: 
>>>>><https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>>>>>
>>>>>
>>>>>List rules & etiquette:
>>>>><https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>www.re-wrenches.org/etiquette.htm
>>>>>
>>>>>Check out or update participant bios:
>>>>><https://mailtrack.io/trace/link/9b840d0d9b3573fe10be9ca23650f9910436d5fb?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=125e41a41f5138ad>www.members.re-wrenches.org
>>>>_______________________________________________
>>>>List sponsored by Redwood Alliance
>>>>
>>>>List Address: 
>>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>>
>>>>Change listserver email address & settings:
>>>><https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>>>
>>>>
>>>>List-Archive: 
>>>><https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>>>>
>>>>
>>>>List rules & etiquette:
>>>><https://mailtrack.io/trace/link/37c2fa3cce2cec32c9af29b35805b1166887102d?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=f5a9d67705ba6495>www.re-wrenches.org/etiquette.htm
>>>>
>>>>Check out or update participant bios:
>>>><https://mailtrack.io/trace/link/9b840d0d9b3573fe10be9ca23650f9910436d5fb?url=http%3A%2F%2Fwww.members.re-wrenches.org%2F&userId=1613865&signature=125e41a41f5138ad>www.members.re-wrenches.org
>>>_______________________________________________
>>>List sponsored by Redwood Alliance
>>>
>>>List Address: 
>>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>>
>>>Change listserver email address & settings:
>>><https://mailtrack.io/trace/link/3edab27b5ab293b8ed7e9b72f6b21719374c3d42?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4d8b59c3f4041e3e>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>>
>>>List-Archive: 
>>><https://mailtrack.io/trace/link/46525d1ae98ac2c9b206af627e181a5e7abef1f9?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=f1379328237c52bb>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>>
>>>List rules & etiquette:
>>><https://mailtrack.io/trace/link/e5dd443e106ab9262a64531e245e33cacc6439c3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1ff02acb7afaa5ce>www.re-wrenches.org/etiquette.htm
>>>
>>>Check out or update participant bios:
>>><https://mailtrack.io/trace/link/df1a46cc62f80e77abb320b6b58d2daa1df33313?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5658938ab50f2b2d>www.members.re-wrenches.org
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address: 
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><https://mailtrack.io/trace/link/d637b44281f438904170f585d45de0c029d858d0?url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&userId=1613865&signature=4e891bb2cdab5fbc>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: 
>><https://mailtrack.io/trace/link/e6c3b50ab784871396cf8aa61952a354fd078c8c?url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&userId=1613865&signature=5c6459243bdea642>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><https://mailtrack.io/trace/link/e5dd443e106ab9262a64531e245e33cacc6439c3?url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&userId=1613865&signature=1ff02acb7afaa5ce>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><https://mailtrack.io/trace/link/df1a46cc62f80e77abb320b6b58d2daa1df33313?url=http%3A%2F%2Fwww.members.re-wrenches.org&userId=1613865&signature=5658938ab50f2b2d>www.members.re-wrenches.org
>>
>>
>>
>>
>>
>>
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address: 
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>>List-Archive: 
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170830/bcb7f610/attachment-0003.html>


More information about the RE-wrenches mailing list