I think the factors you have to consider include:

- the number of conductors in the trench,

-are they in a jacketed cable,

-are they separate conductors,

-are they considered "closely bundled",

-what is the distance of the conductor system once it exits the ground 
before entering a conditioned space, and will it be in conduit.

Chris


On 8/5/2017 5:36 PM, Corey Shalanski wrote:
> How should we treat direct burial wires in a trench for ampacity 
> derating purposes?
> - Should they be considered "in a raceway or cable"? [NEC 310.15(B)(3)(a)]
> - If it is determined that "spacing" must be maintained, what minimum 
> spacing is acceptable/permissible?
>
> I would be interested to hear what means and methods others have used 
> to deal with this issue.
>
> --
> Corey Shalanski
> Joule Energy
> New Orleans, LA
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-- 
Christopher Warfel, PE
Entech Engineering, Inc.
401-466-8978

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170806/da63c2d6/attachment-0003.html>


More information about the RE-wrenches mailing list