[RE-wrenches] Generator choice for Sunny Island

Wesley Kennedy hathasolar at yahoo.com
Tue Jul 25 07:56:58 PDT 2017


One often overlooked detail with SI is it uses the EU standard 10 hour battery rate rather than the US standard 20 hour rate. If you input the 20hour rate as battery capacity then that throws off the SOC calculation. 

-Wes
303-653-3073


> On Jul 25, 2017, at 4:16 AM, Drake <drake.chamberlin at redwoodalliance.org> wrote:
> 
> If there is a grid connection, does the built in battery charger in the Sunny Islands sufficiently make up for any deficit in the AC coupled charging algorithm? 
> 
> Thanks,
> 
> Drake 
> 
>  04:59 PM 7/24/2017, you wrote:
>> I have had generally a good experience with Sunny Island battery charging.  There are definitely way too many parameters to set, but their charging algorithm is designed to bring batteries up to ~90% on the "boost" charge (every 1-2 days), 95% on their "full" charge (typically every 10-14 days) and 100% on their "equalize" charge (typically 120 or 180 days for flooded batteries). It is a different algorithm than any other battery inverter that I've programmed, and I was very skeptical when I first used a SI, but over the years, it does seem to maintain the batteries well (equalize is generally disabled on sealed batteries).  They claim it is the best method, but I do not have enough data points to determine that it works better or worse than the more traditional "bulk/absorb/float" setup. 
>> 
>> Howie
>> 
>> On Mon, Jul 24, 2017 at 4:26 PM, Tom Duffy <Tom at solar-biz.com> wrote:
>> 
>> 8 hours at least but 24 would be more accurate 
>> 
>> Â 
>> 
>> Kind regards
>> 
>> Â 
>> 
>> Tom Duffy
>> 
>> Senior Solar Design Engineer
>> 
>> <140488d7.jpg> 
>> 
>> Your 5-star rating really matters to us. Click to rate! Solar Biz™ team works hard to provide you the best customer service. If we don't deserve a 5-star rating, please contact us directly.  We'll do what it takes to win your approval.
>> 
>> Please note my new E-Mail
>> 
>> E-Mail: tom at solar-biz.com
>> 
>> Main Number: 888-826-0939
>> 
>> Panama Office: 507-836-5588 X 122
>> 
>> Direct Toll Free: 888-503-6772
>> 
>> International: 575-539-2111 X 122
>> 
>> SKYPE Address: thesolarbiz (e-mail first)
>> 
>> I love nuclear energy! It's just that I prefer fusion to fission. And it just so happens that there's an enormous fusion reactor safely banked a few million miles from us. It delivers more than we could ever use in just about 8 minutes. And it's wireless!"Â 
>> 
>> Confidentiality Notice: This message including any attachments is for the sole use of the intended recipient and may contain confidential and privileged information. Any unauthorized review, use, disclosure or distribution is prohibited. If you are not the intended recipient, please contact the sender and delete any copies of this message.
>> 
>> Â 
>> 
>> Â 
>> 
>> From: RE-wrenches [ mailto:re-wrenches-bounces at lists.re-wrenches.org] On Behalf Of Ray
>> Sent: Monday, July 24, 2017 3:24 PM
>> To: re-wrenches at lists.re-wrenches.org
>> Subject: Re: [RE-wrenches] Generator choice for Sunny Island
>> 
>> Â 
>> 
>> My experience with Sunny Islands are that their SOC can be off by quite a bit. Unfortunately with sealed batteries, you can't check SG with a hydrometer to confirm, and tweak the settings.  Probably the best you could do, is shut the system down and let the batteries sit for long enough to take voltage readings to double check the SOC. 
>> 
>> I found systems that the SI thought it was close to full, but the batteries were actually only at 60%.
>> 
>> R. Ray
>> Walters
>> 
>> Chief Technical Officer,
>> RemoteSolar.com
>> 
>> BS Mech Engineering,
>> 1988
>> 
>> Former NABCEP Certified,
>> 2004-2016
>> 
>> Licensed Master ELectrician,
>> Colorado
>> 
>> 303
>> 505-8760
>> 
>> On 7/24/17 2:16 PM, August Goers wrote:
>> 
>> Hi Drake, 
>> 
>> Â 
>> 
>> Good questions. Yes, the taper charge appears to be working well. I've been to the site a couple of times where loads were low, irradiance was high, and battery SOC was ~90% and the Sunny Boy was just covering the load and a little trickle charge. 
>> 
>> Â 
>> 
>> I have noticed that the SOC seems to max out around 90 to 92% - that seems to be the case with Sunny Islands in general. I'm not enough of a battery expert to know if this is a good thing or not. I do know that I custom programmed in all the AGM battery parameters and set max voltages. I also disabled equalize mode since I couldn't find any literature from US battery on recommendations for their AGM. 
>> 
>> Â 
>> 
>> August
>> 
>> 
>> August Goers
>> 
>> Luminalt Energy Corporation
>> 
>> o: 415.641.4000
>> 
>> m: 415.559.1525
>> 
>> www.luminalt.com
>> 
>> Â 
>> 
>> Â 
>> 
>> On Mon, Jul 24, 2017 at 5:36 AM, Drake < drake.chamberlin at redwoodalliance.org> wrote:
>> 
>> Are you getting a good taper charge with this system? Are the batteries reaching a decent state of charge from the AC coupled connection with the inverter?
>> 
>> Thanks,
>> 
>> Drake 
>> 
>> 
>> 
>> 
>> At 11:08 AM 7/23/2017, you wrote:
>> 
>> August,
>> 
>>             Of course the genny itself has its own emission of noise but the environment its in certainly will affect its overall "annoyance level".  Backed up to metal container is a negative, I can't tell from the photo if the Kohler is on the side away from most of the public, probably don't have to go on, you must have thought of these things....it could have its own (partial?)enclosure with some sound deadening qualities.  Hondas are a little quieter but not that much, hopefully the darn thing doesn't have to come on, eh?
>> 
>> Nice set-up.
>> 
>> Bill
>> 
>> Feather River Solar Electric
>> Bill Battagin, Owner
>> 4291 Nelson St.
>> Taylorsville, CA 95983
>> 530.284.7849
>> CA Lic 874049
>> www.frenergy.net
>> 
>> On 7/21/2017 11:39 AM, August Goers wrote:
>> 
>> All,
>> 
>> I thought I'd provide an update on our setup since we've completed the install and commissioning. More or less, the installation went well. We did have one of the US Battery AGM L16 batteries dead on arrival with a bad cell. That bad battery screwed up the state of charge (SOC) calculations in the Sunny Island and made the SOC reading jump from ~ 80% to 19% in just a couple of minutes. It was easy to find the bad battery - all the batteries were about 6.5 v with the bad battery reading about 4.5 v. We pulled that battery out of the string for warranty replacement and are currently running it with seven batteries at 42 v nominal. It's cool that the Sunny Island allows for this. Other than that, the frequency shift derate between the Sunny Island and Sunny Boy is working perfectly and the system has more than enough capacity to run the loads during the summer months. I'd say the Kohler generator is the nice unit although it is a little loud for this application. If I had to do this portable application again, I'd probably just go with the Honda 7000.
>> 
>> Thanks for your help! August
>> 
>> 
>> ---
>> This email has been checked for viruses by Avast antivirus software.
>> https://www.avast.com/antivirus
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> 
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> 
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
>> Â 
>> 
>> 
>> 
>> 
>> 
>> _______________________________________________
>> 
>> List sponsored by Redwood
>> Alliance
>> 
>> Â 
>> 
>> List Address:
>> 
>> RE-wrenches at lists.re-wrenches.org
>> 
>> Â 
>> 
>> Change listserver email address &
>> settings:
>> 
>> 
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>> 
>> Â 
>> 
>> List-Archive:
>> 
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>> 
>> Â 
>> 
>> List rules &
>> etiquette:
>> 
>> 
>> www.re-wrenches.org/etiquette.htm
>> 
>> Â 
>> 
>> Check out or update participant
>> bios:
>> 
>> 
>> www.members.re-wrenches.org
>> 
>> Â 
>> 
>> Â 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> 
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>> 
>> 
>> 
>> Content-Type: image/jpeg; name="image003.jpg"
>> Content-Disposition: inline; filename="image003.jpg"
>> Content-ID: <image003.jpg at 01D30491.30D830C0>
>> X-Attachment-Id: 2bbdfcc76930a8e2_0.0.1
>> 
>> 
>> _______________________________________________
>> List sponsored by Redwood Alliance
>> 
>> List Address: RE-wrenches at lists.re-wrenches.org
>> 
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>> 
>> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>> 
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>> 
>> Check out or update participant bios:
>> www.members.re-wrenches.org
> _______________________________________________
> List sponsored by Redwood Alliance
> 
> List Address: RE-wrenches at lists.re-wrenches.org
> 
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
> 
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
> 
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
> 
> Check out or update participant bios:
> www.members.re-wrenches.org
> 
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170725/33f26f3b/attachment-0002.html>


More information about the RE-wrenches mailing list