[RE-wrenches] Generator choice for Sunny Island

Dave Angelini Offgrid Solar offgridsolar at sti.net
Fri Jun 16 07:55:42 PDT 2017


I use that also Kevin and a place in Maine sells the Honda EU7000i
converted for propane ready to go. Let me know and I will look up the
name. --Dave


> You could use a 2 -> 3 wire converter such as the Atkinson GSCM module
> that will take the 2 wire output from the SI and convert to 3-wire to
> control a gasoline generator such as the Honda EU7000 series, or
> Cummins/Onan makes a good line of gasoline generators. It may be very hard
> to find a gas generator that has 2 wire native remote start. That is more
> common with larger propane or diesel generators.
>
> Kevin
>
> From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
> Behalf Of August Goers
> Sent: June-16-17 7:22 AM
> To: RE-wrenches <re-wrenches at lists.re-wrenches.org>
> Subject: Re: [RE-wrenches] Generator choice for Sunny Island
>
> Thanks for the good feedback folks!
>
> We are using a Sunny Island setup because we had access to a free Sunny
> Island and Sunny Boy being scrapped from another site. Otherwise I was
> definitely planning on going with a Outback DC coupled system.
>
> I think the trick here is trying to find a portable generator that has a
> two-wire start option. I’m looking through the usual genny suppliers and
> nothing has presented itself so far. Anyway, I’ll keep looking and will
> check out Chris’ suggestion on the nexus controller and Generac propane
> unit as well.
>
> FYI, here is a link to what the portal is like. It’s going in National
> Park land by the Golden Gate Bridge so I hope we can pull it together!
> http://www.sharedstudios.com/
>
> August
> Luminalt
>
>
> From: RE-wrenches
> [mailto:re-wrenches-bounces at lists.re-wrenches.org<mailto:re-wrenches-bounces at lists.re-wrenches.org>]
> On Behalf Of Chris Mason
> Sent: Friday, June 16, 2017 4:56 AM
> To: RE-wrenches
> <re-wrenches at lists.re-wrenches.org<mailto:re-wrenches at lists.re-wrenches.org>>
> Subject: Re: [RE-wrenches] Generator choice for Sunny Island
>
> To my limited mind, the whole 120V sunny island setup is a disaster. Why
> not install a DC coupled 8KW Outback Radian and solve all your problems.
> USe any 240V generator, although finding a 2 wire start gasoline unit may
> be hard. I would use a Nexus controller generac propane generator with
> propane tank, all mounted on the container. I would never design anything
> to use gasoline, it's too dangerous.
>
> On Fri, Jun 16, 2017 at 7:19 AM, Matthew Sirum
> <matthewsirum at gmail.com<mailto:matthewsirum at gmail.com>> wrote:
> Greetings August,
>
> Great thoughts and comments from Brian!  I would also suggest speaking
> with the generator manufacturers' tech/engineering folks regarding the
> 120VAC configuration and to confirm 2-wire start set up once you have
> a brand and model or two in mind.  Generator parts and service
> availability in the region of the project may also drive brand
> selection.  If you need to maximize the inverter's battery charging
> capabilities (depending on battery system charging requirements) you
> may end up needing to look at generators in the 7.5 kW to 8.0 kW
> capacity range to allow for headroom in generator output loading.
>
> Also; I am curious how you arrived at an AC coupled design for this
> project.  I do not know any of the details or specific projects goals
> you are working with, but I would potentially consider a DC coupled
> system design...  DC/DC charge controller(s) would keep the battery
> system charged (and any DC loads operable) even if the Sunny Island
> and/or Sunny Boy(s) have a failure or is taken offline.  If most of
> the AC loads are 120VAC I would consider keeping the inverter AC
> output circuit 120VAC and install a dedicated transformer solely for
> the 240VAC load....  Or perhaps consider a 120/240VAC inverter model.
> Depending on the overall situation a DC coupled system could be more
> resilient.  The dedicated transformer for the 240VAC load could also
> potentially help make the system more robust.  Also; I have spoken
> with a number of folks who have told me they wish the Sunny Island had
> more/better features for generator integration.  I'd like to hear more
> from those who have plenty of experience designing and installing
> systems with Sunny Islands and generators to learn what the current
> thoughts and issues are.
>
> I hope some of these thoughts may be helpful.
>
> Best regards,
>
> ----MATT
>
> Matthew Sirum
> P.O. Box 1227
> Greenfield, MA 01302-1227  USA
> phone: +1.413.773.0611
> email: MatthewSirum at gmail.com<mailto:MatthewSirum at gmail.com>
>
>
> --------  Original Message Below --------
>
> [RE-wrenches] Generator choice for Sunny Island
> August Goers august at luminalt.com<http://luminalt.com>
> Thu Jun 15 09:02:41 PDT 2017
>
> Hi Wrenches, especially those of you who work on off-grid projects,
>
> We have an upcoming off-grid project where we will be powering a storage
> container with electronics in it. The loads are mostly 120 volt but there
> is a 240 volt heat pump that might occasionally run. We’re AC coupling
> the
> Sunny Island with a Sunny Boy PV inverter. So, we’ll be installing a
> Outback PSX-240 autoformer to bump the Sunny Island’s output from 120
> to
> 240 volt.
>
> We need to select a generator for backup. We need a two-wire electric
> start
> (in order to be controlled by the Sunny Island) and preferably a
> generator
> that is okay just running 120 volt loads since the Sunny Islands input is
> only 120 volt. Something in the 3 kVA -7 kVA range should be fine.
>
> Does anyone have experience or ideas about what kind of two-wire start
> generator we might select?
>
> Thanks,
>
> August
>
> Luminalt
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address:
> RE-wrenches at lists.re-wrenches.org<mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm<http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org<http://www.members.re-wrenches.org>
>
>
>
> --
> Chris Mason
> NABCEP Certified Solar PV Installerâ„¢
> Solar Design Engineer
> Generac Generators Industrial technician
>
> www.cometsolar.com<http://www.cometenergysystems.com>
> 264.235.5670
> 869.662.5670
> Skype: netconcepts
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>


Dave Angelini Offgrid Solar
"we go where powerlines don't"
http://members.sti.net/offgridsolar/
e-mail  offgridsolar at sti.net
text 209 813 0060




More information about the RE-wrenches mailing list