[RE-wrenches] Third Radian
Tump
tump at swnl.net
Fri Apr 21 06:43:18 PDT 2017
Ive done this repeatably, when installing multiple inverters, there seems to be no problem w/ the FNDC just the space required. I will come off the battery flag term w/ buss bar stock and install my shunt at that point. you can also look at the midnite 1000A battery enclosure. those damn radian enclosures get really filled really quickly. T
> On Apr 20, 2017, at 11:16 PM, William Miller <william at millersolar.com> wrote:
>
> Friends:
>
> I am designing our first three 8K Radian stack. I think I have a good handle on the plumbing and wiring but I was wondering about one thing: With three Radians and a PV recombiner, we are out of shunt ports on the Flexnet DC. Have any of you dealt with this?
>
> My proposal is to gang the negatives for two or three Radians and run them through a 1000A/100mV shunt. The ratio is the same as the 500/50 offered. Will the FNDC accept that analog input?
>
> Any other considerations that might not be realized at first?
>
> Thanks in advance,
>
> William Miller
>
>
> <image003.jpg>
> Lic 773985
> millersolar.com <http://www.millersolar.com/>
> 805-438-5600
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org <mailto:RE-wrenches at lists.re-wrenches.org>
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html <http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm <http://www.re-wrenches.org/etiquette.htm>
>
> Check out or update participant bios:
> www.members.re-wrenches.org <http://www.members.re-wrenches.org/>
> Tump at swnl.net <blocked::mailto:Tump at swnl.net%22%20%5Co%20%22blocked::mailto:Tump at swnl.net> www.SWNL.net <blocked::http://www.swnl.net/%22%20%5Co%20%22blocked::http://www.swnl.net/>
> Solarwinds Northernlights
> Serving Mid Coast Maine & Northern California
> 207-832-7574 Cl. 610-517-8401
> Blair "TUMP" May
> ******** MAINE'S CHARTER ********
> NABCEP "Certified PV Installer"
>
> ******** MAINE'S CHARTER ********
> Trace Xantrex "Certified" Dealer / Installer"
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170421/46f46834/attachment-0002.html>
More information about the RE-wrenches
mailing list