August;
Thanks for pointing out some of those code references, I'm always
learning new things. In case Eric's situation is not subject to
physical damage (as covered in 230.50) I found that 230.43 lists many
more allowable options for service entrance wiring, but NM still is not
on the list. I think the confusion may be with the definition of
"Feeder". Eric wrote that they tapped into the "feeder" between the
Meter and the Main disconnect. I may be mistaken, but technically that
is not a feeder; it would be considered a service conductor. Service
conductors are from the utility to the main disconnect (service
equipment), while feeders are all the conductors after the Service
equipment. I think the Old school guy might have won that one.
R. Ray Walters
Chief Technical Officer, RemoteSolar.com
BS Mech Engineering, 1988
Former NABCEP Certified, 2004-2016
Licensed Master Electrician, Colorado
303 505-8760
On 4/4/17 5:17 PM, August Goers wrote:
>
> Hi Eric,
>
> Regarding the supply side connection, check out this article:
> http://iaeimagazine.org/magazine/2013/11/16/supply-side-pv-connections-a-closer-look/
>
> Check out 2014 NEC 230.50 – I don’t think NM is allowed. In our neck
> of the woods we need to use RMC or IMC.
>
> Secondly, I’d recommend referring to the NM cable’s spec sheet to
> determine ampacity. Also see NEC 334.80 which limits the ampacity to
> 60 deg C.
>
> 50 A x 1.25 = 62.5, so your NM has to be rated at this or higher.
>
> http://www.southwire.com/products/RomexSIMpullTypeNMBOEM.htm - regular
> NM 60 deg rated #6 55 A
>
> I’m not familiar with 90 degree NM.
>
> August
>
> Luminalt
>
> *From:*RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org
> <mailto:re-wrenches-bounces at lists.re-wrenches.org>] *On Behalf Of
> *eric at harvesthesun.com <mailto:eric at harvesthesun.com>
> *Sent:* Tuesday, April 04, 2017 2:50 PM
> *To:* RE-wrenches <re-wrenches at lists.re-wrenches.org
> <mailto:re-wrenches at lists.re-wrenches.org>>
> *Subject:* [RE-wrenches] NM Cable temp rating, ampacity, application
>
> Hi Wrenchers,
>
> I recently butted heads with an old school electrician who has been
> scrutinizing a recent install (fully permitted & PTO'd last year) and
> I wonder how applicable and valid his concerns are. I'm not interested
> in an ego war with this guy; I just want to be code-compliant and
> safe. This sparky (let's call him Karl) has questioned my
> electrician's (let's call him Dave) use of NM cable on the AC side of
> the solar install.
>
> The first issue that Karl raised was that Dave installed Romex for our
> supply-side connection, i.e., from our fused disconnect to the Polaris
> vampire clamps on the feeder conductors between the meter and the main
> disco. Karl contends that the Romex, by extension off of the utility
> feeders, is now a service entrance conductor and that NEC Article
> 334.12 dictates that Romex cannot be used as service entrance
> conductors. Wondering how you all might interpret this scenario.
> (note: We have the opportunity to pull new conductors, should the
> consensus be that we violated the NEC)
>
> The second issue is that Dave ran 6AWG Romex from the fused disconnect
> to the main breaker in the combining subpanel and landed the circuit
> on a 70A breaker. The inverter circuit is rated at max current of 50A
> continuous. Karl is telling us that the #6 Romex is rated at 60
> degrees and 55 amps. It is my understanding that all NM cable is now
> rated at 90 degrees. However, I also understand that there may be some
> merit to Karl's assessment regarding limited ampacity of the 6AWG
> Romex. Can someone illuminate this issue for me as to whether or not
> NM cable is rated at 90 degrees AND therefore a 6AWG conductor in NM
> cable would have a 75A rating?
>
> Cheers,
>
> Eric
>
> SunHarvest
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170404/efb37c6a/attachment-0002.html>
More information about the RE-wrenches
mailing list