[RE-wrenches] Conduit Bushings

Glenn Burt glenn.burt at glbcc.com
Sat Mar 4 04:22:09 PST 2017


Well, to start it is a 110.3(B) violation to cut the bushings as you describe and install them.

-----Original Message-----
From: "peter.parrish at calsolareng.com" <peter.parrish at calsolareng.com>
Sent: ‎3/‎3/‎2017 14:14
To: "'RE-wrenches'" <re-wrenches at lists.re-wrenches.org>
Subject: [RE-wrenches] Conduit Bushings

Recently we were asked to do a combined inspection and engineering review of a 362.70 kWdc PV system using 5 Sungrow SG60KM-U inverters. We found issues like palm trees and air handling equipment shading significant parts of the arrays, electrician’s tape and palm fronds on the surface of the modules. But we also observed two significant Code violations: PV  source conductors lying on the surface of the torch-down roof and lack of bushings at the connectors on the ends of 2” LFMC. The PV source conductors got secured and we saw bushings threaded onto the ends LFMC connectors.

Upon close inspection we discovered that the bushings had been broken at one point on their circumference, no doubt to simplify their attachment. Their were 11 PV source circuits (22 current-carrying 10 AWG PV Wire conductors.)

Is this a NEC Code violation? If so, what section would we cite? It seems obvious that the bushing had been “modified”, but I would like to be more specific. Or does it come under the workmanship category?

Regards,

- Peter Parrish

Peter T. Parrish, Ph.D., President
SolarGnosis
1107 Fair Oaks Ave.
Suite 351
South Pasadena, CA 91030
(323) 839-6108
Peter.parrish at solargnosis.com
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170304/9209248b/attachment-0002.html>


More information about the RE-wrenches mailing list