This was a not-uncommon issue that would occasionally arise with 
specific washers and the SW series. It often came up with Y2K 
installations. It has nothing to do with voltage /per se/, and the 
inverter is working as it should. The SW is true modified-sinewave (with 
something like 28-42 waveform steps per half-wave). The problem is that 
the electronic controls in the washer aren't compatible with the 
waveform. In short, three options:

1- Sometimes a large electrolytic capacitor across the inverter ac 
output terminals will work. I have seen it work but not always.

2- Try a different brand of washer.

3. Upgrade the inverter to a sinewave unit.

Allan Sindelar, Sindelar Solar


On 2/8/2017 12:10 PM, Lou Russo wrote:
> Aloha All,
>
> I have a client with a old Trace 4024 on a APT center. Everything has 
> worked great for over 20 years. He purchased a new washing machine 
> from Sears that does not want to work. The voltage at the outlet is 
> 117 vac and the Sears guy says that is the issue. When the system is 
> running on the genset (Northern Light 6kW Diesel) we get 121 vac and 
> the washer runs fine. That seems like a very tight voltage window and 
> a issue with the washer not the system. I have seen sensitive 
> electronics go wacky with no N-G bound maybe that is the issue? I did 
> not install the system so I would have go poke around. Any one out 
> there have any ideas?
>
>
> Aloha,
>
> Lou Russo
> lou at spreesolarsystems.com <mailto:lou at spreesolarsystems.com>
> 440 345 6762
> Spree Solar Systems LLC
> CT-34322
>
>
>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>

-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20170208/d7fc59d2/attachment-0002.html>


More information about the RE-wrenches mailing list