Can you come out of the line side tap to the 
lugs, and connect the solar to the breaker 
terminals? This way a retainer clip is not required.

At 11:12 AM 11/30/2016, you wrote:

>Sorry I should have elaborated more from the beginning.
>
>Â
>
>I am using the panel as a service disconnect for 
>a lineside connection (can’t use a 
>fused/bladed disco because of space 
>constraints). Originally I bought a QO 70A 
>panel, but soon realized that the Square D 
>retention clip (PK2MB) is only compatible with 
>their larger panels. So I bought a larger panel 
>(100A 8 Circuit) and then received some feedback 
>that having the open spaces (even if labeled 
>that “Do Not Add Loads”) could raise a flag 
>with an inspector. So then I was back on the 
>hunt for a dedicated 2 Pole 60A or 70A panel 
>with a compatible retention clip for a 30A 
>breaker. Eaton’s retention options only start 
>in the 60A range (the smaller breakers don’t 
>have the hole in them to put the bolt through). 
>Square D said they don’t have an option for 
>their 70A panel. There aren’t any good Siemans 
>distributors near me but I wasn’t finding an 
>option via google for them either.
>
>Â
>
>I talked with another Wrencher on the phone and 
>received this feedback which I’m just going to 
>cut and paste to include it in this thread:
>
>
>“The NEC doesn’t require a hold down clamp 
>for the circuit breaker unless it can be backfed 
>from a multi-mode or stand-alone inverter (690.10(E)).
>
>The language implies that a hold-down is 
>therefore not required elsewhere. Most modern 
>breakers (def. QO’s) are not marked “line” 
>and “load” so no problem there (also in same code section).
>
>Â
>
>Even when it was a requirement for all PV 
>outputs, John Wiles had argued that taking off 
>the panel cover, which required a tool, served 
>as the hold-down, and this was generally accepted.”
>
>Â
>
>So taken that advice I’m back to using the QO 
>70A panel but without a retention clip (or 
>calling the lid the "retention clip").
>
>Â
>
>For what its worth I have passed inspections 
>prior using the retaining clip from a generator 
>interlock kit (QOCGK2C) on a QO 100A panel, but 
>felt like there must be a better option out there....
>
>Adam Katzman
>Autonomous Energies
>PO Box 1245
>Kingston, NY 12402
><http://www.autonomousenergies.com>www.autonomousenergies.com
>(518) 567-1468
>
>
>On Wed, Nov 30, 2016 at 10:45 AM, Drake 
><<mailto:drake.chamberlin at redwoodalliance.org>drake.chamberlin at redwoodalliance.org> 
>wrote:
>Siemens has main breaker retainers. The 
>retainers for QO seem work on some boxes and not 
>others. It doesn't work on 6 space boxes I've 
>purchased, but does work on the 8.
>
>At 10:14 PM 11/29/2016, you wrote:
>
>>Wrenchers,
>>
>>I̢۪m trying to find a 60A 2 Pole Breaker Box 
>>that hashas a compatible retaining clip. The QO 
>>retaining clip (PK2MBCP) seems to only be 
>>compatible with their 4-8 circuit load centers. What are my options? Thanks!
>>
>>Thanks
>>
>>Adam
>>_______________________________________________
>>List sponsored by Redwood Alliance
>>
>>List Address: 
>><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>>
>>Change listserver email address & settings:
>><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org 
>>
>>
>>List-Archive: 
>><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html 
>>
>>
>>List rules & etiquette:
>><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>>
>>Check out or update participant bios:
>><http://www.members.re-wrenches.org/>www.members.re-wrenches.org
>
>
>
>----------
><https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>
>Avast logo
><https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient> 
>
>
>This email has been checked for viruses by Avast antivirus software.
><https://www.avast.com/sig-email?utm_medium=email&utm_source=link&utm_campaign=sig-email&utm_content=emailclient>www.avast.com 
>
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: 
><mailto:RE-wrenches at lists.re-wrenches.org>RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
><http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
><http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
><http://www.re-wrenches.org/etiquette.htm>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
><http://www.members.re-wrenches.org>www.members.re-wrenches.org
>
>
>
>_______________________________________________
>List sponsored by Redwood Alliance
>
>List Address: RE-wrenches at lists.re-wrenches.org
>
>Change listserver email address & settings:
>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
>List-Archive: 
>http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
>List rules & etiquette:
>www.re-wrenches.org/etiquette.htm
>
>Check out or update participant bios:
>www.members.re-wrenches.org


---