[RE-wrenches] Ring Connectors

Allan Sindelar allan at sindelarsolar.com
Mon Nov 14 09:56:52 PST 2016


Will,
1/4" ring by whatever size wire you choose. Del City is a good source - 
www.delcity.net. #153145 is 1/4"/#10AWG; #254145 is same for #8 and 
#255145 for #6.
Standard indent crimper for non-insulated terminals, not the automotive 
type. Mine is a Klein.
Allan

*Allan Sindelar*
allan at sindelarsolar.com <mailto:allan at sindelarsolar.com>
NABCEP Certified PV Installation Professional
NABCEP Certified Technical Sales Professional
New Mexico EE98J Journeyman Electrician
Founder (Retired), Positive Energy, Inc.
*505 780-2738 cell*

**

On 11/14/2016 10:34 AM, Will White wrote:
> Hey Wrenches,
>
> I'm doing an upgrade to an Outback VFX series off-grid system with the 
> flexware boxes.  What type/brand of ring connectors and crimpers do 
> you all use for the DC breakers with the post terminals?
>
> Thanks,
> Will
>
>