[RE-wrenches] Wire nuts

Benn Kilburn benn at skyfireenergy.com
Tue Sep 6 12:01:45 PDT 2016


The reason i'm asking is that the only time i have seen a short,
first-hand, in a wire nut, was because it appeared that one wire was pushed
down rather than binding with the other wire, which would have happened if
the wires were not held tightly when the nut was twisted on.  Also, it was
a stranded wire (that was pushed down) being connected to a solid wire,
which is acceptable, but care must be taken to do it properly.

Also, on all the Ideal wire nut packages I have, the instructions say to
twist the wire nut on until there are two visible twists in the wire.  I
suppose this is to ensure the twist/connection is sufficient to make a
solid connection and perhaps to keep the wires together if the wire nut is
removed.

The ones in this photo do not look like they were installed as per the
instructions, which brings how much attention was put in to installing them
in the first place.

I've always questioned the why wire nuts are cautioned against, especially
considering how many wire nuts are used in residential and commercial
jobs.  I'm sure if there was a legit issue with them then insurance
companies would insist they not be used, such as aluminum wiring?

*Benn Kilburn *
CSA Certified Solar Photovoltaic Systems Electrician, SkyFire Energy Inc
14515 – 121A Ave NW | Edmonton, AB | T5L 2T2
P: 780-474-8992 | F: 888-405-5843 | www.skyfireenergy.com
[image: email] <benn at skyfireenergy.com> [image: facebook]
<https://www.facebook.com/SkyFireEnergy> [image: twitter]
<https://twitter.com/SkyFireEnergy> [image: linkedin]
<https://www.linkedin.com/company/283735?trk=tyah&trkInfo=tarId%3A1408655033432%2Ctas%3Askyfire%2Cidx%3A2-2-5>


[image: SkyFire Energy Logo_horizontal]

*WE HAVE MOVED! Please note our new address above.*

On Tue, Sep 6, 2016 at 12:47 PM, Jerry Shafer <jerrysgarage01 at gmail.com>
wrote:

> All the other nuts are tight so l cant not say it was or not but l see
> this alot and this was one that was caught just at the right time.
> Jerry
>
> On Sep 6, 2016 8:44 AM, "Benn Kilburn" <benn at skyfireenergy.com> wrote:
>
>> Jerry,
>> Can you confirm that this was caused by a failure of the wire nut,
>> itself, and not due to user error (not properly stripping enough jacket,
>>  inserting even length wires and sufficiently twisting on the wire nut)
>>
>> Benn Kilburn
>> SkyFire Energy Inc.
>> 780-906-7807
>>
>> On Sep 6, 2016, at 12:32 PM, Jerry Shafer <jerrysgarage01 at gmail.com>
>> wrote:
>>
>> Wrenches
>> Better pic
>>
>> On Sep 5, 2016 4:52 PM, "Jerry Shafer" <jerrysgarage01 at gmail.com> wrote:
>>
>>> To my fellow wrenches
>>> It comes up every so often and with DC, I will not use, approve or pass
>>> any wire nuts on any DC side. Some say its OK but the facts are they will
>>> fail, this connection was just six years and when l opened the junction box
>>> it was glowing and by the looks of it has for some time. There are 8
>>> strings 2 per string and thats a 12.5 % failure rate (the other one was
>>> completely distroyed) not to mention the fire hazard in a PVC junction box.
>>> Please pass this along and tell everyone to stop using these.
>>> Jerry
>>>
>> <2016-09-06 08.29.40.jpg>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re
>> -wrenches at lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive: http://www.mail-archive.com/re
>> -wrenches at lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive: http://www.mail-archive.com/re-wrenches@lists.re-wrenches.
> org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160906/59f96c2d/attachment-0002.html>


More information about the RE-wrenches mailing list