[RE-wrenches] Pass through/transition box for Enphase
Glenn Burt
glenn.burt at glbcc.com
Thu Aug 11 17:53:06 PDT 2016
Interesting product, and good for standard stranding conductors, as their UL
486C certification attests.
They are however a screw to conductor connection device and will have the
same limitation when used with finely stranded conductors as the standard
Polaris splices.
The Polaris grey connectors have a metal sleeve already in the port as part
of the device, which the screw crushes against the fine stranded conductors
- essentially performing the same function as installing ferrules on the
conductors.
Glenn
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Chris Worcester
Sent: Thursday, August 11, 2016 10:33 AM
To: 'RE-wrenches'
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
When we have the Enphase 240 VAC trunk line branching in two directions we
use these 300V rated Alumiconn 3 port connectors, to make them up to the #10
THWN-2. These are a scaled down version of the Polaris insultaps.
http://www.kinginnovation.com/products/20/3-port-alumiconn
Chris Worcester
Solar Wind Works
NABCEP Certified PV Installer
Office 530-582-4503
Cell 530-448-9692
Fax 530-582-4603
www.solarwindworks.com
chris at solarwindworks.com
From: RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] On
Behalf Of Jeremy Rodriguez
Sent: Wednesday, August 10, 2016 6:32 PM
To: RE-wrenches
Subject: Re: [RE-wrenches] Pass through/transition box for Enphase
How about these?
https://idealind.com/us/en/products/wire-termination/set-screw-connectors/se
t-screw-connectors/set-screw-wire-connectors.aspx
Jeremy Rodriguez
Solar Installation And Design Expert
All Solar, Inc.
1463 M St
Penrose Colorado 81240
Sent by Jeremy's iPhone. Sorry for typos and shorthand!
On Aug 8, 2016, at 2:00 PM, Benn Kilburn <benn at skyfireenergy.com> wrote:
Din rail mounted terminal blocks.... Weidmuler WDU6 or WDU10, depending on
the wire size you are using.
Benn Kilburn
SkyFire Energy Inc.
780-906-7807
On Aug 8, 2016, at 12:49 PM, Jason Szumlanski
<jason at floridasolardesigngroup.com> wrote:
I'm looking to bring 8 Enphase 240V circuits in multiple conduits into an
enclosure inside the attic where I can transition to Romex. I'd rather use
some kind of rail mounted terminals in an enclosure or something rather than
making splices in a generic j-box. I'm not looking to combine circuits -
just transition from THWN to Romex and keep things neat an organized.
Any suggestions?
Jason Szumlanski
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
_______________________________________________
List sponsored by Redwood Alliance
List Address: RE-wrenches at lists.re-wrenches.org
Change listserver email address & settings:
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
List-Archive:
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
List rules & etiquette:
www.re-wrenches.org/etiquette.htm
Check out or update participant bios:
www.members.re-wrenches.org
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160811/ea3f7a5e/attachment-0002.html>
More information about the RE-wrenches
mailing list