Hi Jason,



We’re in a territory where we can’t run Romex (NM) directly into Soladecks
because of the wet location issue. I actually think inspectors are easing
up on enforcing this particular code grey area, but nonetheless we haven’t
run NM directly into Soladecks. I imagine that using a regular NM cable
clamp connector would work.



When we do run NM, we terminate it in indoors in a permanently accessible
box typically located in the attic or on the ceiling or wall by the roof
penetration location. Then, we run EMT through the roof and to our rooftop
J-box. THWN-2 is run between these two boxes. Then, the microinverter (or
ACPV) wire is spliced to the THWN-2 at the rooftop J-box. Yes, this means
three wire types for each install! We’re using splice cap crimp connectors
for all of our splices which we’re very happy with:
http://www.idealindustries.ca/products/wire_termination/terminals_crimps/crimp_connector_splice_cap.php
- ferrules are available for fine stranded conductors.



August



*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Jason Szumlanski
*Sent:* Tuesday, July 26, 2016 9:08 AM
*To:* RE-wrenches
*Subject:* [RE-wrenches] New Construction Enphase Romex / NM



It seems like most jurisdictions are now allowing a transition to Romex in
a Soladeck box where the Romex enters the attic immediately and runs in
protected space all the way back to a load-side interconnection or combiner
panel. Two issues:



   - How are you bringing the Romex into the back of the Soladeck? Standard
   metallic strain relief or strain relief with rubber compression gasket or
   other means?
   - Assuming you can't use a Soladeck due to the roof type and are using a
   standard PVC roof junction box mounted to a rail with conduit to get into
   the attic, are you transitioning from Enphase cable to THWN-2 in the j-box,
   then installing a PVC or metallic pass-through box in the attic to
   transition to Romex? Even though it's a short distance from the j-box to
   the point where the conduit penetrates the roof plane, it's still a wet
   location so Romex isn't allowed. In fact, some jurisdictions are requiring
   this even for Soladeck boxes because they consider the Soladeck an
   enclosure in a wet location so the inside must also be considered a wet
   location, making the transition to Romex improper in their opinion.