Ash,

I'd look at the Solar Edge 5000 inverter with P300 optimizers or the SMA
5000TL.  Either way you end up with two strings, one old and one new.  Less
work with the SMA route.  Better performance with the SE. With the SE route
the owner could actually see the performance improvement on the older SW175
string.  The owner can find a new home for the old inverter on EBAY

Carl Adams
SunRock Solar
NABCEP Certified PV Instsller
On Jun 21, 2016 6:13 PM, "Jerry Shafer" <jerrysgarage01 at gmail.com> wrote:

> I have 12 sharp 72 cell and that only 444 voc so that should not be an
> issue, yes l know he has SW but they are very close
> Jerry
> On Jun 21, 2016 10:31 AM, "Brian Teitelbaum" <bteitelbaum at aeesolar.com>
> wrote:
>
>> Hi Ash,
>>
>>
>>
>> Are you sure that there are 12 of the SolarWorld 175’s on a single string?
>>
>>
>>
>> Those were 72-cell modules, and I would think that having 12 in series in
>> CO would see open-circuit voltages over 600 VDC at least on some occasions.
>> That’s 864 cells in series, with would be about equal to having 14.4
>> typical 60-cell modules in series. That sounds too high to me for CO.
>>
>>
>>
>> One option would be to reduce the number of 175’s to 10 (720 cells in
>> series) and match them with 12 of the 60-cell modules (also 720 cells in
>> series). The older modules are 5” cells, so their amperage would be lower,
>> but as long as you get the voltage as close as possible it should be fine.
>> Of course, this doesn’t account for degradation, so you may want to do some
>> actual voltage measurements on the old modules.
>>
>>
>>
>> One thing though – since twelve 280W modules is about 3360W, and you have
>> a 3kW inverter, there really isn’t enough room to add. The older Sunny Boys
>> had a much narrower MPPT voltage range, so I doubt that you could use
>> strings shorter than nine 60-cell modules. I don’t see how you would be
>> able to add much to the old inverter anyway. Adding a second inverter
>> system may be your only option, unless you can find some used 175’s. 18 or
>> 20 of the 175’s, in two strings, should work fine on the 3kW Sunny Boy.
>>
>>
>>
>> Brian Teitelbaum
>>
>> AEE Solar
>>
>>
>>
>>
>>
>> *From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
>> Behalf Of *Ash Bowersock
>> *Sent:* Tuesday, June 21, 2016 12:48 PM
>> *To:* re-wrenches at lists.re-wrenches.org
>> *Subject:* [RE-wrenches] Add-On to DGT, string inverter, w/Different
>> Modules on 2nd string
>>
>>
>>
>> Good day RE Wrench crew,
>>
>> I’ve got a client whom installed a 2kW array with a 3kW SunnyBoy inverter
>> a number of years back. Due to the age of the system I assume it is single
>> MPPT. The client oversized his inverter in the hopes of using it for this
>> future expansion (and unfortunately his installer went along with it). The
>> original modules were 12 SolarWorld 175’s I believe, and we would be
>> looking at adding SolarWorld 280’s more than likely. To me it is clear that
>> this is poor design practice and not something I am willing to do. My
>> recommendation is a micro-inverter system that we tie in w/his existing
>> using an AC Combiner. But the client wants to know exactly why we don’t
>> want to just add a second string of 12 SolarWorld 280’s to his 6 year old
>> SunnyBoy inverter.
>>
>> Can someone please give me a technical reason why mixed modules on a
>> string inverter is “poor design practice”?
>>
>> The more technical and dry an explanation, the better ;)
>>
>> If you can’t convince them, bore them to tears with the details.
>>
>>
>>
>> Ash Bowersock
>> Senior System Designer
>>
>> [image: RGS Energy] <http://www.rgsenergy.com/>
>>
>> 833 W. South Boulder Road | Louisville, CO 80027
>> tel 303.222.8387
>>
>> *RGSEnergy.com* <http://www.rgsenergy.com/>
>>
>> *Confidentiality Note: *This e-mail message may contain confidential or
>> legally privileged information and is intended only for the use of the
>> intended recipient(s). Any unauthorized disclosure, dissemination,
>> distribution, copying or the taking of any action in reliance on the
>> information herein is prohibited. E-mails are not secure and cannot be
>> guaranteed to be error free as they can be intercepted, amended, or contain
>> viruses. Anyone who communicates with us by e-mail is deemed to have
>> accepted these risks. RGS Energy is not responsible for errors or omissions
>> in this message and denies any responsibility for any damage arising from
>> the use of e-mail. Any opinion and other statement contained in this
>> message and any attachment are solely those of the author and do not
>> necessarily represent those of the company.
>>
>>
>>
>>
>>
>> _______________________________________________
>> List sponsored by Redwood Alliance
>>
>> List Address: RE-wrenches at lists.re-wrenches.org
>>
>> Change listserver email address & settings:
>> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>>
>> List-Archive:
>> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>>
>> List rules & etiquette:
>> www.re-wrenches.org/etiquette.htm
>>
>> Check out or update participant bios:
>> www.members.re-wrenches.org
>>
>>
>>
> _______________________________________________
> List sponsored by Redwood Alliance
>
> List Address: RE-wrenches at lists.re-wrenches.org
>
> Change listserver email address & settings:
> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org
>
> List-Archive:
> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html
>
> List rules & etiquette:
> www.re-wrenches.org/etiquette.htm
>
> Check out or update participant bios:
> www.members.re-wrenches.org
>
>
>
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160621/b67fc53c/attachment-0002.html>


More information about the RE-wrenches mailing list