Hi Ash,



Are you sure that there are 12 of the SolarWorld 175’s on a single string?



Those were 72-cell modules, and I would think that having 12 in series in
CO would see open-circuit voltages over 600 VDC at least on some occasions.
That’s 864 cells in series, with would be about equal to having 14.4
typical 60-cell modules in series. That sounds too high to me for CO.



One option would be to reduce the number of 175’s to 10 (720 cells in
series) and match them with 12 of the 60-cell modules (also 720 cells in
series). The older modules are 5” cells, so their amperage would be lower,
but as long as you get the voltage as close as possible it should be fine.
Of course, this doesn’t account for degradation, so you may want to do some
actual voltage measurements on the old modules.



One thing though – since twelve 280W modules is about 3360W, and you have a
3kW inverter, there really isn’t enough room to add. The older Sunny Boys
had a much narrower MPPT voltage range, so I doubt that you could use
strings shorter than nine 60-cell modules. I don’t see how you would be
able to add much to the old inverter anyway. Adding a second inverter
system may be your only option, unless you can find some used 175’s. 18 or
20 of the 175’s, in two strings, should work fine on the 3kW Sunny Boy.



Brian Teitelbaum

AEE Solar





*From:* RE-wrenches [mailto:re-wrenches-bounces at lists.re-wrenches.org] *On
Behalf Of *Ash Bowersock
*Sent:* Tuesday, June 21, 2016 12:48 PM
*To:* re-wrenches at lists.re-wrenches.org
*Subject:* [RE-wrenches] Add-On to DGT, string inverter, w/Different
Modules on 2nd string



Good day RE Wrench crew,

I’ve got a client whom installed a 2kW array with a 3kW SunnyBoy inverter a
number of years back. Due to the age of the system I assume it is single
MPPT. The client oversized his inverter in the hopes of using it for this
future expansion (and unfortunately his installer went along with it). The
original modules were 12 SolarWorld 175’s I believe, and we would be
looking at adding SolarWorld 280’s more than likely. To me it is clear that
this is poor design practice and not something I am willing to do. My
recommendation is a micro-inverter system that we tie in w/his existing
using an AC Combiner. But the client wants to know exactly why we don’t
want to just add a second string of 12 SolarWorld 280’s to his 6 year old
SunnyBoy inverter.

Can someone please give me a technical reason why mixed modules on a string
inverter is “poor design practice”?

The more technical and dry an explanation, the better ;)

If you can’t convince them, bore them to tears with the details.



Ash Bowersock
Senior System Designer

[image: RGS Energy] <http://www.rgsenergy.com/>

833 W. South Boulder Road | Louisville, CO 80027
tel 303.222.8387

*RGSEnergy.com* <http://www.rgsenergy.com/>

*Confidentiality Note: *This e-mail message may contain confidential or
legally privileged information and is intended only for the use of the
intended recipient(s). Any unauthorized disclosure, dissemination,
distribution, copying or the taking of any action in reliance on the
information herein is prohibited. E-mails are not secure and cannot be
guaranteed to be error free as they can be intercepted, amended, or contain
viruses. Anyone who communicates with us by e-mail is deemed to have
accepted these risks. RGS Energy is not responsible for errors or omissions
in this message and denies any responsibility for any damage arising from
the use of e-mail. Any opinion and other statement contained in this
message and any attachment are solely those of the author and do not
necessarily represent those of the company.
-------------- next part --------------
An HTML attachment was scrubbed...
URL: <http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20160621/c2c672f1/attachment-0002.html>


More information about the RE-wrenches mailing list